Discuss Will my circuit take appliances drawing 6000 watts? (None sparky) in the The Welcome Forum area at ElectriciansForums.net

G

gazawee

FORGIVE MY IGNORANCE (I'M NOT A SPARKY) JUST WANT TO UNDERSTAND BETTER


I just purchased a catering trailer that is already wired up.

The road side supply is a 32amp (commando socket).

Consumer unit in the trailer is fitted with 1 x 63amp / 30mA RCD Incomer (Trip Switch) plus 1 x 32 amp Miniature Circuit Breaker (for sockets) and 1 x 6 amp Miniature Circuit Breaker (for Lighting).

I thought it a little strange but the external socket on the trailer that will connect to the road side supply is a 16amp commando socket.

I was told that the wire from the external socket to the consumer unit is 6mm and I expect the wire running to the sockets from the consumer unit to be 2.5mm.

Given that I need to be able to plug in to the sockets, appliances that will collectively draw up to almost 6000 watts,



1. Do I need to change my external commando plug from a 16 to a 32

2. If the wires to the sockets are 2.5mm, will they fry when everything is plugged in and do they need to be changed to 6mm?
 
Hi gazawee,

6000 watts will draw approximately 27A if it is all on together (and this obviously doesn't include any lighting). I'm not going to attempt to use diversity to say otherwise because without a list of appliances, it's impossible.

The cable connecting the socket to the consumer unit may be pushed beyond it's limits, depending on the installation method. If it comes through the wall from the socket, is clipped directly to the surface and goes straight into the CU, it's more than ample (47A).

1. If it was my trailer then I would be changing the socket for a 32A, and of course upgrading the flying lead that connects it to the source of power.
2. This depends if they are wired as a ring final circuit or a radial. The rating of the MCB suggests they might be wired as a ring final, but if they aren't, depending on installation method, the cable may only be able to handle 20A and would fry.

My suggestion is have a look for a local member and have them give it the once over to get a definitive answer.
 
@gazawee I have altered your thread title and changed it from 6000 amps to watts, it could have generated some strange replies. I presume it was a typo.
 
Okay just checked the appliances and it should be closer to 5300 (not including lights)

Plugged in appliances:

Fridge 130w
Freezer 150w
Microwave 2600w
Rice Maker 1950w
Soup Kettle 400w

Also has a maypole BATTERY CHARGER 6A 12V (Model P7416)
 
Okay just checked the appliances and it should be closer to 5300 (not including lights)

Plugged in appliances:

Fridge 130w
Freezer 150w
Microwave 2600w
Rice Maker 1950w
Soup Kettle 400w

Also has a maypole BATTERY CHARGER 6A 12V (Model P7416)

So, rough current usage:-

Fridge - 0.6A
Freezer - 0.7A
Microwave - 12A
Rice maker - 8.5A
Soup kettle - 1.8A
Charger - I've assumed basic step down transformer, roughly 20:1, thus 6A output assuming 100% efficiency will draw 0.3A - but I've used 1A for the calculation

Using the diversity calc for socket outlets/fixed equipment for a small shop, 100% of largest load + 75% of remaining gives a maximum demand after diversity of around 21.45A.

So I would still upgrade the socket and flying lead and have a local check it out for you because if it's a radial socket circuit, depending on installation method, it could potentially do damage to the cabling. Paying someone for an hour of their time to check it out is by far the best option... it's much cheaper than a new trailer and without seeing it, it's impossible to give a definite answer about whether it can handle it.
 

Reply to Will my circuit take appliances drawing 6000 watts? (None sparky) in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
463
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
581
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
915
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock