Discuss Wiring a new delay switch in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
I need to replace a faulty light delay switch with a replacement. The current switch has 3 wires that must be several years old as all are red wires (one is marked with blue - perhaps from a more recent electrician?). 2 wires are going into the "com" switch and one into "on". I want to replace with a switch that has just a "live in" and "live out" terminal, therefore asks for only 2 wires and says not to fit an earth / neutral wire. Any suggestions for how to do this – I’m guessing I attach the red one from the “com” into “live in” and the one from “on” to the “live out” and then to tape up the blue labelled wire and not use it?! Advice would be appreciated!
 
sounds about right, but a bit of trial and error is indicated.
 
Thanks Telectrix... and it's perfectly safe to just tape up and tuck away the "blue" wire?
stick a single choc connector or a wago on it. by rights, you should also diss. the other end of it and connect both ends to earth if there is the facility to do so.
 
Why are you ditching the red Taped blue? If it is currently in with the other red in the common then in may well be a loop out to other lighting.
 
As westward10 says even if it is sleeve blue it must be connected directly to another line conductor and so would trip the circuit breaker if it were a neutral conductor.
Test for voltage between the the cores and also to earth, both in the switch (off and on) and out of the switch, this should tell you which ones are which, I would expect that it is a loop supply and a switch wire so all live when the switch is on.
 
Your description is unclear.

The number of wires used is irrelevant. It's the number of terminals used that matters. If the original switch had wiring to two terminals, then connect the same wires into the two terminals on the new switch.
 

Reply to Wiring a new delay switch in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi Total novi e but have wired multiple light switches previously and survived :) I've bought a nice WiFi enabled dinner switch for a new LED...
Replies
11
Views
955
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
Replies
6
Views
675
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
600
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
619
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
967

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock