Discuss Wiring lights on exposed beam in flex in the UK Electrical Forum area at ElectriciansForums.net

Steve T

-
DIY
Reaction score
117
Hi all,

I'd like to replace some MR16 halogen fittings on an exposed wooden beam to new GU10 fittings which I will be fitting led lamps into. The current fittings are wired in 2 core flex as they're only 12v, can't see a problem with that.

For the new lights I'm planning on using black 3 core 1.0mm flex, so effectively the flex will be fixed wiring, even though its exposed and clipped direct to the beam. As I understand it, it is permitted for use in fixed wiring. I will also be using ferrules on the screw connections in the lights. Reason I don't want to use T&E is because the beams are dark brown and I think black flex would look nicer and be easier to hide, it will be seen unfortunately as there is a mezzanine above the beam the lights are on. As I understand it, 1.0mm is the minimum size cable required for lighting circuits hence my choice of 1.0mm flex, however I have seen it mentioned that if you're using flexible cable you could use as low as 0.75mm which is rated at 6A so in theory would be ok on a 6A mcb when clipped direct in free air, which would be preferable as its easier to hide.

Can anyone please confirm which is the correct size to use, 0.75mm or 1.0mm, and that flex is ok to use in this situation?

Thanks for any replies!
 
I would probably be inclined to install a fused connection unit where the transformers lived (you're going to be installing a junction box of somekind I'm guessing), drop in a 3A fuse and use 0.75mm flex.

Table 4F3A does give a CCC for 0.75mm of 6A.
 
I would probably be inclined to install a fused connection unit where the transformers lived (you're going to be installing a junction box of somekind I'm guessing), drop in a 3A fuse and use 0.75mm flex.

Table 4F3A does give a CCC for 0.75mm of 6A.
Thanks, that's a good shout, I might be able to hide an FCU at the end of the beam where the transformer was, just not sure whether the edges of the box would go over the edges of the beam, will have to check tomorrow. I was going to use one of the old style 6A brown JBs, which are of course very small. Failing that I could probably just use 1.0mm flex and live with the fact that it will be bigger than 0.75mm, probably better than having an unsightly FCU. I also wasn't particularly happy that the 0.75 flex is rated the same as the MCB, not that the lights should draw anywhere near 6A but still.
 

Reply to Wiring lights on exposed beam in flex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
756
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
495
Hi all, Got an antique light fitting that for some reason she wants putting up (can't say I love it haha) however it didn't come with any...
Replies
9
Views
3K
I have a spare 2.5mm 3 core flex cable. Can I use it for an outdoor light? It will be connected a junction box that's already supplying...
Replies
2
Views
997
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top