davek

Hi all
been called out to a boiler replacement with the above boiler. The problem is it wont run on heating only. have check wiring and all I can spot is that from controller there is no wire going from HW OFF to cylinder stat terminal 2 and grey on valve. Any thoughts and no spare cores in original wiring.
regards
Dave
 
spoke to Worcester apparently the lp on the boiler need run direct to pump so will give it a try tomorrow,
cheers
Dave
 
Hi.... On a y-plan you need the cable from the hw off connection on the programmer to the grey on the valve and number 2 on the cylinder stat to power the valve into heating only... You will not get it to work correctly in another way
 

Reply to worcester greenstar ri Y-Plan in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
977
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
630

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock