The installation is TT.

The meter box has been moved by the DNO. The tails will now be >3m so I will be fitting a switch fuse. I was planning on removing the DP switch in the switch fuse and replacing with a 100mA S type RCD. I would have put one in place of the main switch in the CU so this seems like a better idea as it will give greater protection to the tails as well.

My question is, do the tails and main earth still need to enter the main consumer unit through a gland or could they just go in through one of the knock outs? I always use a gland to keep them secure as if the tails ever came loose inside the CU the main fuse would not trip, however in this case the RCD would trip, so is the gland necessary?
 
For the price of a tails gland just use one imo...

Or I guess you could just bring the tails through the same knock out as the cables if it’s easier
 
For the price of a tails gland just use one imo...

Or I guess you could just bring the tails through the same knock out as the cables if it’s easier
Why wouldn’t you? End of the day it gives you the proper IP rating, and you’ll probably have a gland in your van anyway? I’m not clued up on TT systems but for the sake of a few pence, I’d be putting a 32mm ct gland in.
It's purely logistics, not the cost of one gland. Without going in to detail it would be far easier and neater to use a knock out.
 
No problem using a knockout however I just like using the glands as it makes a neat entry and helps to keep the tails in place to stop untoward movement in the main switch terminations.
 
How are you going to earth the armour, if you don't use a gland? (by which I mean an SWA gland, rather than a compression gland). The armour is an exposed-conductive part, and needs to be earthed.
 
How are you going to earth the armour, if you don't use a gland? (by which I mean an SWA gland, rather than a compression gland). The armour is an exposed-conductive part, and needs to be earthed.
Sorry Steve, I should have been more precise with my wording. I'm using tails nor SWA. I don't think I've ever glanded off SWA without the correct gland
 
Apologies, the fault is mine. You didn't mention SWA, I don't know why I assumed it. Brain was on auto. My bad, sorry.

As you were... :)
 
I would always advocate the use of a tails gland. I would also always advocate the use of an S-type RCCB upfront of the distribution board(s) in TT systems.
 

Reply to Would I still need a gland for the tails and earth on this TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
902
I have added a consumer unit and an earth stake to this so called temporary supply. This is a full rcbo board apart from the mcb to the spd...
Replies
11
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock