I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin
 
I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin

What is the potential danger you have identified?
 
I was thinking the potential danger is the switching capacity isn't high enough in case of a fault.

That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?
 
That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?

There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.

So the load is under the 60 amp rating of the main switch.
 
you can't do anything till you've assessed the load on this CU. get the clamp meter out at midnight.
 
There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.

So the load is under the 60 amp rating of the main switch.

which heaters are thermostatically controlled, so the full 52A will only be seen when they first switch on. therefore, no code.
 
I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin
 
I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin

no problem. the consultancy invoice is in the post. :smilewinkgrin:
 

Reply to Would you code a 60 amp main switch been fed from a 100 amp BS1361 in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock