I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin
 
I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin

What is the potential danger you have identified?
 
I was thinking the potential danger is the switching capacity isn't high enough in case of a fault.

That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?
 
That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?

There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.

So the load is under the 60 amp rating of the main switch.
 
you can't do anything till you've assessed the load on this CU. get the clamp meter out at midnight.
 
There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.

So the load is under the 60 amp rating of the main switch.

which heaters are thermostatically controlled, so the full 52A will only be seen when they first switch on. therefore, no code.
 
I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin
 
I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin

no problem. the consultancy invoice is in the post. :smilewinkgrin:
 
I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin

Whether you code it or not is your decision.
When deciding on coding an observation you will find it helps to ask yourself the same questions I have done above. For C1 'what is the immediate danger here?', C2 'what is the potential danger?' for C3 'what improvement do I recommend/can this situation be improved?'
 
Well 230v is the declared single phase voltage throughout the country now even though nothing has really changed [apart from the network becoming ever more stretched to the limit] so that's what we have to base calculations on, I see what you're saying about the heaters though.
 
I have never seen the voltage at 230v, and am measuring everyday, the lowest I have seen it is 235v. Never seen 216v, but 250v yes. 315v but that was ug fault lol
 
Well 230v is the declared single phase voltage throughout the country now even though nothing has really changed [apart from the network becoming ever more stretched to the limit] so that's what we have to base calculations on, I see what you're saying about the heaters though.

That is not the declared voltage, it is the nominal voltage, something which some jobsworth in an office has written down and is impossible to implement. Nothing has changed because it cannot be changed, the whole country has substations with their output fixed at 250/433, there's nothing any jobsworth penpisher can do about that!
It doesn't change the basic physics though, If the stated power rating is at 240V you cannot just replace 240 with 230 in the calculation. The power dissipated will be less at 230V so the current which flows will be less.
 
Last edited:
Ironically the supply here was always 230V unlike the 220V in the south of Ireland and the 240V in Britain, and so harmonisation had no effect here!
 
That is not the declared voltage, it is the nominal voltage, something which some jobsworth in an office has written down and is impossible to implement. Nothing has changed because it cannot be changed, the whole country has substations with their output fixed at 250/433, there's nothing any jobsworth penpisher can do about that!
It doesn't change the basic physics though, If the stated power rating is at 240V you cannot just replace 240 with 230 in the calculation. The power dissipated will be less at 230V so the current which flows will be less.

Yes DECLARED as the NOMINAL voltage, only because the distribution network is so stretched and it gives them more leeway, I often see low to mid 230s here in Cornwall. And what's a penpisher ? :confused: :wacko:
 
Yes DECLARED as the NOMINAL voltage, only because the distribution network is so stretched and it gives them more leeway, I often see low to mid 230s here in Cornwall. And what's a penpisher ? :confused: :wacko:

If it has been declared as a nominal value then it is still only nominal! It has nothing to do with the **** state of the networks, the nominal voltage was changed to 230 by the penpushers in Europe, it was not changed to give anybody more leeway as the voltage has always been permitted to drop as low as 230.

It should have said penpusher
 
Yes I know, and of course it's purely coincidence that they can get away with a lower voltage- it can quite legitimately be under 230 now, the network is in lovely condition.
 

Reply to Would you code a 60 amp main switch been fed from a 100 amp BS1361 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hi guys - seeking an opinion or possibly experience of the same issue. I have a spark engaged to do a fair bit of upgrade, been here for 35 years...
Replies
38
Views
9K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top