Discuss Wylex 80A 30ma rcd - and known issues? in the Industrial Electricians' Talk area at ElectriciansForums.net

polo1

-
Arms
Reaction score
633
Hi folks,
carrying out an EICR yesterday. Board is a split Wylex (main switch with the rcd covering half the board). All circuits are on the rcd side.
Problem I encountered was trying to take 'no trip' Zs readings, the rcd always trips. The meter (1520) is definitely on the correct setting. Neutrals in the correct bar, TNS supply.
Tried reading both at the rcd and remotely. In normal operation, customer advises that there has been no history of tripping.
Am I missing something obvious, or is it a faulty rcd?
 
It's usual.
You have a load still connected.Could be a PIR, LED lamp, timer.
Anything that may have a circuit board with reference to earth.
 
Never had an issue with connected loads before, is this a "Wyex" issue? Wouldn't ramp test either. 8.5Mo l/n to earth on the whole board. Don't think it's my tester, as I proved it on my own board when I got home.
 
Last edited:
Hi Polo

Its possible that the 15mA injected for the loop test is pushing the RCD over its limit (with normal leakage with all circuits on RCD)I would try switching off all the other MCB's and test each circuit individually.

Tested loads of Wylex boards and have had this due to above also 6A MCB;s sometimes trip on no trip ZS test !

You say the RCD would not Ramp test I would be looking again at that issue.

Did the RCD test values come out OK ?
 
As said there could already be earth leakage on the circuits and the test is just pushing it over edge especially if all circuits are on 1 RCD. I have had a RCs tripping with trip lock on due to a load on the circuit, I have found that fridges are the usual course . Try turning all the other circuits off when doing the test
 
Guys, thanks for the feedback and suggestions. I'm back next week so will try dissing loads and do one circuit at a time.
Forgot to mention, couldn't get x1/x5 results either.
 
Guys, thanks for the feedback and suggestions. I'm back next week so will try dissing loads and do one circuit at a time.
Forgot to mention, couldn't get x1/x5 results either.

If that is the case then i think taking the loads off should solve the problem , You always take the load of when testing RCD trip time , you will see they differ by quite a lot if you have a load on the circuit and can sometimes fail to operate
 
Sorry to ask this, I'm sure you checked... If you get your N and E leads the wrong way round (e.g. where the leads plug into your MFT) then this will cause the RCD to trip every time. I have a Kewtech; it has different sockets for dead tests and live tests, so often a "no trip Zs" is the first live test that uses all 3 leads (for high current Zs, e.g. Ze, and PFC, you join N and E leads together, so it doesn't matter!). The blue and green can look quite similar in reduced light. Just sayin' :)

I have a Wylex 80A 30mA RCD in exactly the same board you're describing. No issues, test it once a month.
 

Reply to Wylex 80A 30ma rcd - and known issues? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock