Hello all,

I am looking to install an xpelair 12v fan in a bathroom with a humidity sensor (model no. 92970AW). I can't quite work out from the instruction manual whether the humidity sensor is in the fan itself or in the transformer. due to the size of the bathroom and the position of the bath it is necessary to mount the transformer outside the bathroom where a transformer mounted humidity sensor won't be of much use! So if anyone has installed one of these before I would grateful if you could let me know where the sensor resides.

Also on the subject, I am providing a dedicated circuit protected by RCD for the fan which I'll run to a 3a fused spur outside the bathroom. Is an isolator required in this case? I only ask as the tenants aren't the type you'll see polishing their doorstep and in my experience of working in less than savoury households, the fan iso's are more often than not switched off. Would an unswitched fused spur be satisfactory?

Regards
 
The humidity sensor is mounted in the fan, there will be a small grille on the fan behind which is the sensor.
Most fan instructions require a DP isolator with minimum 5mm opening gap, this function would be provided by the RCD. Therefore a fused spur would be acceptable.
The other common recommendation is a triple pole isolator so that the fan can be worked on safely, however this function can also be covered by the RCD.
Some fan manufacturers do not require a local 3A (or 1A) fuse, I cannot remember for xpelair, I think they say you can use a lighting circuit, so so long as the MCB is 6A then you would be OK, but do check the instructions.
 
Dunno, I'm more inclined to fit extra low voltage extractor fan above shower head (including bath with additional shower head) rather than low voltage regardless of zones etc, but I'm willing to be convinced otherwise?
 
Dunno, I'm more inclined to fit extra low voltage extractor fan above shower head (including bath with additional shower head) rather than low voltage regardless of zones etc, but I'm willing to be convinced otherwise?
Why is this.
 
Surely a mains voltage fan is only suited to Zone 2 at best and the OP wants to mount his fan in Zone 1 ?

What makes you state this Dave,is it belief that they are not permitted or personal preference?

Edit
Bit late with the question for you Dave, Richard has let the cat out of the bag :)
 
An IPX4 fan at 230V can be used in zone 1, it is one of the list of 230V items that can be be installed as fixed permanently connected equipment.

Sorry Richard [and Des] , I worded my post badly. I'm aware that the regs permit this but don't like putting a mains voltage fan directly above a bath or shower. Probably a bit silly on my part when you think of the mains voltage [and high current drawn] in an electric shower. :)
 
I am going for a 12v fan as the tenants don't strike me as the type of people who have much of a sense of self preservation... They probably have cash4claims on speed dial so don't fancy leaving 240v at arms reach for them. They have previously taken a ladle or other large kitchen utensil to smash the smoke alarms off the ceiling. Imagine doing that when they are all lathered up and super conductive!
 
Sorry Richard [and Des] , I worded my post badly. I'm aware that the regs permit this but don't like putting a mains voltage fan directly above a bath or shower. Probably a bit silly on my part when you think of the mains voltage [and high current drawn] in an electric shower. :)

Concur with Dave, no rational reason.

My irrational morbid fear isn't helped any by manufacturers statements;

- Vent-Axia still recommends that any fans installed within Zones 1 and 2 should be SELV (Safety Extra Low Voltage

- Xpelair LV100 12V Safety Extra Low Voltage (SELV) fans offer complete peace of mind as they are specifically designed to be
installed directly in or over the splash area zone 1 in complete safety


- Manrose range of 12 volt S.E.L.V. (Safety Extra Low Voltage) fans are specifically designed for the safe ventilation of toilets, bathrooms and shower rooms and can be fitted within the splash area with absolutely no risk of
electric shock.

All (I think) Shower Light fans are selv?

However, I think it's time I manned up, and faced these nonsensical fears, put them behind me and start installing IPX4 fans in zones 1 & 2 as recommended by 701.512.2 :eek:
 
No go with what you're comfortable with Midwest, not all 230v fans are rated IPX4 and there's nothing wrong with improving on the minimum requirements stated in BS7671.
It's fine to fit a mains incoming LED downlighter above a shower though, I often do but make sure it's 1P65 and fed via an RCD.
 

Reply to Xpelair 12v humidistat fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
625
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
606
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
924
Hi. My current axial Xpelair model 92614AW ground floor bathroom extractor fan is installed in zone 1 and doesnt work efficiently at all. Its wall...
Replies
22
Views
2K
Hi I have bought a new bathroom fan to replace a faulty one. I don't have much cable available (emerging from wall) and it won't stretch to the...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock