Evening all,

My first post here, hope you are all welcoming :)

I have my QS assessment coming up next week with the NIC.

Question is, I am going to a property where I installed a 2way board, split the tails, upgraded the bondings etc. Straight forward job but the resident has a 24 hour oxygen supply running from DB1. Lovely old lady, I didn't want to turn the power off for her when I did the works, I tested my new board (db2) but with all the earths connected in as mentioned above I didn't want to turn the power off. 0.13 ohms, TNc-s.. all good.

I am just wondering if I am not able to turn the power off on DB1, therefore not disconnect any main earths, will the NIC let me test the ZE as an 'operational limitation' or as a zDb with it being a domestic property?

I understand 0.13 may not be a true representative of the earth fault path with the parallel earths connected, just wondering what I will say to the inspector when he asks me to perform a Ze test??

Long winded I know, but if you was in my shoes on the day what would be the correct way of going about this?

Many thanks all :)
 
It would be unreasonable to make you perform the test or have the results on the test sheet. You may not cut power without the permission of the installation owner.
You've done the right thing and as said above, you may just get asked to talk through the test procedure.
 
Note on the cert that Ze was taken with parallel paths in place as no permission to isolate was granted by the owner.
 
Can’t see them asking you to do something to the detriment of the occupier. I’ve only been through the process once but get the impression they like to keep things quick and simple in order to tick the boxes and get on to the next appointment. ?
 
I wouldn't worry too much, You can always do Zs at the board with explanation.

They dont have to get you to do every test, in my experience they do a selection from what is reasonable or practical on the day. they do always go through safe isolation though, so maybe demonstrate that on your home CU? or on DB2 at the site?
You can prove DB2 is isolated and check testing equipment against a known live supply DB1
On my visit I did the following tests.... i should add that on this install I couldnt verify where the water bodning was due to it being a property with carers and disabled resident. I had a 10mm at the board but couldn't find where it went too. my work was all in the garage. Assessor had no issue with that and accepted that real life is different to the books.
1581629727388.png
 

Reply to Ze Test, NICEIC QS ASSESMENT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
880
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock