hi, just been to a Call-out, mobile home site. one homeowner has had a faulty socket replaced and the electrician who did the job, quite correctly filled out a MWC, problem is his Zs reading was 51.2 ohms. now, the supply comes approx. 100yards from the cut-out ( which is boxed on the supply pole) in 2 core 6mm SWA, using the armour as earth ( circa 1960's). I checked his readings with MFT and got 49.5ohms, then measured Ze at the cut-out, 0.22ohms PME system. think it's pretty clear, it's the resistance of 100yds of armour that is the problem. the home has a 30mA RCD , front end 16th ED. so my query is: do i leave well alone, or dis. PME and convcert home to TT. which will hopefully make the installation comply. replacing the cable is not a option, considering that half the park will have to be excavated.
 
50Ω is a big reading - is it worth looking for a corroded high resistance joint at one end or the other that can be re-terminated?
 
2-core swa using armouring as cpc should give a resistance of about 1 ohm over 100m, probibly should be worth a look for corrosion somewhere on the joints!
 
points taken. will check both end connections 2morrow. told home owner there's nothing to woory about as she has RCD. with regard to your post, nick. DNO converted to PME with that cable already in place. so, as per my orig. post, do you think i should convert the home to TT and dis the home end of the armour?
 
I'd make the glands off again if there is enough movement to do so and see what if that makes any difference to the readings.
 
i forgot to mention. the cable is not glanded. the armour is earthed at both ends with jubilee clips. suspect oxidation, but it started to p*** down so that,s first thing to check tomorrow
 
Ah ok in that case I would get the clips off and give it a dam good wire-brushing or going over with emery paper to clean up the faces and see if that helps.
 

Reply to Ze & Zs-- unacceptable readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
an eicr was carried out to an industrial plant area were the zs readings were all high readings above the maximum for a tns installation i...
Replies
9
Views
2K
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock