Discuss Zs and more Zs in the Australia area at ElectriciansForums.net

these figues that the Supply authority will say depending on the supply.

Be carefull with TT systems as the supply authority will state 21 Ohms this is the resistance of there earth rod at the transformer. When you install an earth rod the combined resistancce of your rod + theres must be under 200 ohms.
 
From what I understand, their argument is that EAWR doesn't allow live working.
As such the Ze and Zs tests are not allowed, as Ze can be obtained through enquiry and Zs by calculation.


The EAWR does not allow live working yes i agree However it does allow for live testing as the live parts are exposed but there is no interference with the system exept the insertion of GS38 probes connected to a meter all of which comply to current safety standards.
 
Be carefull if relying on inquiery as i have found wrong presentation of cable heads with no earth at all.

If you are unwilling to pull fuses then note on a PIR as a limitation and take a ZS at the nearest point of origion where access can be obtained. (normally the main isolator.)
 
Yes, Rb = max 21 Ohms

Ra+Rb should be under 200 Ohms.

Or under 100 Ohms if you read BS 7430

Someone just removed the post I'm replying to, it looks like I've lost the plot!
 
Last edited:
The EAWR does not allow live working yes i agree However it does allow for live testing as the live parts are exposed but there is no interference with the system exept the insertion of GS38 probes connected to a meter all of which comply to current safety standards.

As IQ has already posted, the EAWR do not distinguish between working and testing.
 
Sorry thought we'd strayed onto wether to test live or calculate Zs,model forms in Appendix 6 just asks for Zs doesn't state has to be measured or calculated.
 
EFLI testing is live testing. This Live testing involves working on or hear live conductors. It is unlawful to work on or near live conductors under Regulation 14 of the EAWR 1989 unless " it is unreasonable in all the circumstances for it to be dead".



Pinched the above section from an IET forum on this sam subject.

THe key words are "is it un reasonable in all circumstances for it to be dead" how do you do a dead ELI or RCD test? It has to be live so then work out a risk assesment. GS38 probes ect which means you then comply with EAWR
 
BS7671 allows for Ze and PFC to be obtained by enquiry, as such it is not whether it is reasonable for it to be dead, but whether it is neccessary at all.
RCDs and Zs at socket-outlets can be tested with out the need to expose live conductors, as would functional testing of switches and RCDs.
Zs for other circuits can be obtained by calculation.
As such, it would appear that the only test required to be conducted live with exposed conductors, is polarity of supply.
 
In my opinion itn is always better to measure the Ze it is allowed and gives a good indication of the quality of earthing. I have found that the supply authority do not always know the supply arrangement or give the stock answer of " we dont have to supply an earth"
 
i learnt to test Zs and all other live tests by testing on live circuits. i also learnt to ride a bike with wheels on it. i shall continue to ride a bike with it's wheels attached, same as i will continue to test as i've always done. seems the next generation of sparkys won't be able to install anything in case the screwdriver slips cuts their lily whites.
 
. i also learnt to ride a bike with wheels on it. i shall continue to ride a bike with it's wheels attached, same as i will continue to test as i've always done. seems the next generation of sparkys won't be able to install anything in case the screwdriver slips cuts their lily whites.

Telectrix, how on earth do you ride a bike without the wheels?
 

Reply to Zs and more Zs in the Australia area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
483
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
955
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
896
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock