Discuss Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net

Ze is only at the origin, the rest are Zs.

Measure/calculate the R1+R2 for each distribution circuit and add the Ze. (Zs=Ze+(R1+R2))
 
I have a ccu with a Ze of 0.09 and it's supplying another ccu which that board supplies multiple other CCUs I was wondering how I would work out my zs and ze on the other boards?

Ze only exists at the origin, e stands for external.

In an existing installation you measure Zs at each board.

If this is at the design stage then you need to use the calculated impedance of the circuit and add it to the Ze quoted for the supply.
 
Ze is only at the origin, the rest are Zs.

Measure/calculate the R1+R2 for each distribution circuit and add the Ze. (Zs=Ze+(R1+R2))
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?
 
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?

Yes it does become the Zs at the DB, but obviously that is also the Zs of the distribution circuit because they are one and the same thing.

Strictly speaking 'Zs at DB' or 'Zdb' are not correct terminology, much like 'ring main' instead of 'ring final circuit', everyone knows what is meant by it, it's commonly used, but it's not correct terminology.
 
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?
Each board would have its own Zs, sometimes referred to a Zdb. I think we're saying the same thing.
 
Yes it does become the Zs at the DB, but obviously that is also the Zs of the distribution circuit because they are one and the same thing.

Strictly speaking 'Zs at DB' or 'Zdb' are not correct terminology, much like 'ring main' instead of 'ring final circuit', everyone knows what is meant by it, it's commonly used, but it's not correct terminology.
But, 'Zs at DB1, 2, 3', whatever, is a statement...nothing wrong with the terminology, whatsoever.
 
Last edited:

Reply to Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
585
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
507
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
787
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
336
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock