If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
Yes, the Zs at the DB goes in the "Zs at DB" box, the clue is in the name, it's not a trick question.
Discuss Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net
If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
Nope, unless it's not connected to origin.If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
I agree with ipf, but there will always be a Jobsworth that disagrees with this though.But, 'Zs at DB1, 2, 3', whatever, is a statement...nothing wrong with the terminology, whatsoever.
Yes, the Zs at the DB goes in the "Zs at DB" box, the clue is in the name, it's not a trick question.
Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointless.Nope, unless it's not connected to origin.
You do your PEFC with all parallel paths connected at the origin not a ZE test .The Ze test determines the resistance of the earthing conductor external to the installation and confirms an earth connection to the installation hence it’s done with no parallel paths connected.Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointless.
If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
I'm talking about Schedule of test result - Zs at DBYou do your PEFC with all parallel paths connected at the origin not a ZE test .The Ze test determines the resistance of the earthing conductor external to the installation and confirms an earth connection to the installation hence it’s done with no parallel paths connected.
Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointlessI'm talking about Schedule of test result - Zs at DB
The test carried out at the origin DB is the Ze not Zs. This is done with parallel paths removed to confirm the continuity and loop impedance of the DNO supply.ill just take it you don't have to do Zs at DB at origin DB, unless anyone says differently.