Just though, could it be argued that the Zs you're interested in is that relating to the fuse in the FCU, which for a 13A BS1362 is 1.8ohms for a 0.4 second disconnection time..

Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.
 
Reading is 0.79 at the furthest point, like I said it’s the only socket on the circuit, and is about 10-15mtr run from its DB

Hi,

You say it's a radial & that it is the only socket on the circuit & that Zs is 0.79

Yes a 30mA RCBO max is 1667 ohms


Just out of interest what csa is used on the radial? because if it's in 2.5mm on a 32A RCBO then the OCPD is to high for the cable ie. highest is 27A on clipped direct for t&e.

ie. an A2 radial is 4mm on a 30/32 amp OCPD, Zs stated in BBB for type C is 0.68 ohms (4mm is what I'm assuming is used on your radial)

An A3 radial is in 2.5mm on a 20 amp OCPD, Zs stated in BBB for type C is 1.09 ohms
So a 20A type C RCBO Zs at 80% is 0.872 ohms
 
Last edited:
Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.
That's why I like this game, and this forum.

You have to think as often there are many answers that will work, some unnecessary solutions and sometimes it's fine as it is.
 
What about fault protection up to the spur.

Fair point, I had it in my head that spur origin was back to back, or side by side with the FCU in the same CSA cable as the original circuit. Then the new run to a DP isolator for the stair lift. In this I wouldn't be losing a great deal of sleep.

However it could equally be spurred, 10m cable run with FCU at the end, in which case you're right.

Any case it's on an RCBO so who cares, apparently.
 
In this case then due to bad design/change in Regs the high Zs is through no fault of yours.

In this case I would utilise the RCBO for fault protection although. This is not permitted in Bs7671 so will need to be recorded on the MWC as a deviation.
 
Changing it to a B Type may import nuisance tripping when the stairlift is starting.

Only a possibility but personally based on the info we have got I would leave it as a C Type and utilise the RCD for fault protection and note the deviation on the cert.
 

Reply to Zs reading does not meet current regs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, DIY'er here looking for some advice. In March 2023 we should be getting 5.5kW of solar PV going on the roof feeding into the current...
Replies
4
Views
1K
I was surfing through one of the electrical training groups on Facebook yesterday and came across this question from an AM2 prep course: There...
Replies
7
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Edited - please read right to the end! Grateful for any advice regarding CT metering which seems to be generating inaccurate/implausible...
Replies
25
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock