Discuss Zs reading in workshop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

PHS

-
Reaction score
4
The last problem I have to finish the paperwork is that I have a Zs @DB reading from the house CU of 0.31ohms with a Ipf @ DB of 0.74 ka.
On the test result sheet for the workshop, which has a 40amp rcd, 2 x 20amp socket radials and a 6amp lighting curcuit, what figures do I use to add to the R1/R2 readings to get me the Zs figures needed?
and what figures go into the Zs and Ipf @ DB box on the sheet for the workshop.
If what I have writen doesn't make sence please say and I will try to explain better.

I am thinking its the same figures as the house
Cheers guys
 
Ze +((R1+R2) for the feed to the workshop) = Zdb at the workshop
Zdb at the workshop + ((R1+R2) for the workshop circuits) = Zs for the circuits
Assuming the above Zs cannot be measured, also assuming that I'm reading your question correctly.
 
The workshop is fed from a 40amp non protected breaker in the house and I got an (R1+R2) reading of 0.15 from the feed into the workshop (if it was just feeding a socket for instance as a radial)
but it is feeding a new cu in the workshop.
Do I add the 0.15 to the 0.31 to get the figure needed to add to the R1+R2 readings of the radials and lighting circuit is what I'm getting at really or am I missing the point altogether?
 
I'm at a loss to understand what bit of #2 you don't get mate, let me know and I'll try to explain it a bit more clearly.
 
The workshop is fed from a 40amp non protected breaker in the house and I got an (R1+R2) reading of 0.15 from the feed into the workshop (if it was just feeding a socket for instance as a radial)
but it is feeding a new cu in the workshop.
Do I add the 0.15 to the 0.31 to get the figure needed .


yes, just as trev said.
 
So, by measurement or by calculation?
Either way it's not that hard is it? It sometimes seems that way when you've been looking at it and disappearing up your own backside though
 
So, by measurement or by calculation?
Either way it's not that hard is it? It sometimes seems that way when you've been looking at it and disappearing up your own backside though

Measurement in the end. Was just not thinking straight, to many things in my head!!
 
Measurement in the end. Was just not thinking straight, to many things in my head!!

Sometimes you can look at something for too long and because your head is up your backside you just go round and round in circles mate. We've all been there and done that.
 

Reply to Zs reading in workshop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house. My mistake was not doing a Zs before I...
Replies
39
Views
5K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
Hello, I created this account as I have ran into a huge issue with my electric bill. I have been living at my house for 1 year right now. Every...
Replies
13
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock