Discuss ZS Testing in the UK Electrical Forum area at ElectriciansForums.net

With a 20 amp pulse down the earth I would defo recommend unplugging appliances , not only because you could damage some appliances , you will be inducing a live supply to the casing of class 1 appliances ,,,
 
I always do. If the ELI is high there could be a shock risk while doing the test. There is always a risk that someone could be in contact with the equipment.
 
I always do. If the ELI is high there could be a shock risk while doing the test. There is always a risk that someone could be in contact with the equipment.

How do you work that out ?

If the ELI is high enough to allow >50V touch voltage on the CPC the test aborts, my meter allows me to set this at either >= 25V or >= 50V, I would assume most other meters do the same or similar.
 
How do you work that out ?

If the ELI is high enough to allow >50V touch voltage on the CPC the test aborts, my meter allows me to set this at either >= 25V or >= 50V, I would assume most other meters do the same or similar.

If the CPC was totally open circuit there has to be a shock risk.
 
If the CPC was totally open circuit there has to be a shock risk.

But the test aborts in that case.

What I was getting at was if you look at all of the calcs in the regs concerning Bonding, sup bonding, RCDs, Earth rods on TT, they are all concerned with stopping the touch voltage from rising above 50V , exactly the same as your meter does during the test, for the same reasons.

By your reasoning you could have a fully compliant system (albeit on the edge), that could be err... dangerous in the event of a fault, which is precisely what the regs are designed to prevent. no?
 
But the test aborts in that case.

What I was getting at was if you look at all of the calcs in the regs concerning Bonding, sup bonding, RCDs, Earth rods on TT, they are all concerned with stopping the touch voltage from rising above 50V , exactly the same as your meter does during the test, for the same reasons.

By your reasoning you could have a fully compliant system (albeit on the edge), that could be err... dangerous in the event of a fault, which is precisely what the regs are designed to prevent. no?
yep...

i read that one...and thought it was drivvel....
 

Reply to ZS Testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
839
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
619
Hi all, Not sure if asking about rates is allowed, but I'm wondering what people's thoughts are on chargeable rates for PAT testing. Baring in...
Replies
5
Views
808
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
566

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock