yes on tt system if ze less than 1667 then everythink ok.because rcd will disconnect in 0.2 thus satisfying 0.4 disconnection time
 
415.1.2

The use of RCD's is NOT recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in sections 411 to 414.

To my mind that means getting your Zs and disconnection times within those specified irrespective of RCD's (TT's being the exception)
 
the maximum zs reading on a tn circuit incorporating an rcd shall be 1667 as per iee regs.therefore zs readings redundant on 99% of domestic installations
 
That's not said in the regs. Only regarding TT. But that is because on TT system you are going to get such variable readings from your earth rod they allow you to conform with formula
Ra In > 50v.
reversing the formula
50v/0.03mA= 1667 ohms. That the maximum Zs with an RCD that allows unto the safe touch voltage.
On a TN system you aren't going to get nowhere near that figure.
 
reg 411.5.3 rcd protection 0.2 dissconection any system


I disagree...that is under the heading of TT system.

As I said 411.4.9 leans towards the statement of "where an RCD is used (for whatever reason) to fulfill 411.3.2.2 (where the loop impedance could be too high for the MCB/fuse alone to achieve it) then the values of EFLI in table 41.5 may be applied for RCD's to 61008 & 61009 for final circuits upto 32A.
 
if a tt system ze up to 1667 will disconnect in 0.2 then a tn max 0.80 can,t fail to can it on an rcd

Nick, I don't think anyone is saying the device wouldn't physically operate, they are looking for a regulation to support the entry of 1667
in the max Zs box.

Also, Ze or more correctly Ra on a TT system is not recommended to be above 200 Ohms for stability (Table 41.5, note 2)
 
lets face it if you can have 200 ohms on a stake c/w rcd then anything lower tncs is no problem.live neutral fault no problem as poses no danger to public.overload on mcb will deal with that
 
Rcds can and do fail

I personally believe a TN system with a failed Rcd, and Zs readings outside of permitted limits,would appear to be a much greater danger than the TT with a failed Rcd

I did read that the High fault currents on a TN system where the Rcd is designed to operate, at say 30m/amp,it can damage those electronics more readilly than the low fault current TT system

Where the RCd has bit the dust
If someone bridged a live earth fault,the Tn system would allow a massive fault current,where as the TT would be just a tickler :)

I use the tabulated values for TN systems and the 1667 exclusively for TT
 
I did read that the High fault currents on a TN system where the Rcd is designed to operate, at say 30m/amp,it can damage those electronics more readilly than the low fault current TT system

I know we're drifting off-topic here but where did you read this?
 
I was speaking to a sparkie other day that said he has had a few RCD's go belly up on a x5 test. I do not and never will place my trust in an RCD of any type to protect people against shock protection, I don't do anywhere the number of installs you guys do, but the amount of failures out of the box frankly frightens me, Hager, MK, RCBO's and RCD's all failed miserably on a number of occasions, technology is a good thing but not always the best thing
 
As IQ electrical has stated there is no specific reg pointing to this, you'd like to think that the regs would think logically and go with the trend of 'We are trying to push the use of RCDs to cover majority of circuits in a domestic situation, perhaps we should provide a Zs table with RCD protection for TN systems.' have they not done this because they want us to use the different MCB values regardless?
Des could you please explain why it would be more dangerous on a TN? (not questioing just don't understand )
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
733
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
692
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock