Discuss Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

bs7671

Hi there I have another question for you guys.What is the maximum Zs values for different circuit breakers i.e type B,C,D also where would we find them and why the difference?
 
the difference is due to the different characteristics of the breakers. the Zs max. is the max. you can allow for the particular breaker to disconnect in the permitted time
 
I want to find a table or something so I can see the Ka ratings as per different device type.Or at least someone to explain it in simpleton terms
 
It's the 'on no trip' bit that you need to question.

Most no-trip readings are much higher than conventional Zs readings using a full-current test.

There's also a chance that the RCD is distorting your reading.
 
New posts

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
825
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
785
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock