Discuss Zs Values. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

you don't. Zs readings are dependet on the cpc. Zs= Ze+(R1+R2). you don't have an R2 so you can't measure Zs
 
Last edited:
either that or put N/A. don't forget to fix label on CU stating "NO CPC ON LIGHTING CIRCUIT" and note it on your cert. make sure that there are no metal fittings or switches. and that the switch pins screw into non-conductive lugs and don't bottom out on the back box .
 
Last edited:
It depends I take it your not installing it new, or adding to it as you wouldn't be able to with like that, so your doing a PIR in which case it would need to be marked down as a code deviation code 2 I think but maybe a 1 not to sure but defo a big bad deviation.

Unless none of the lights require a cpc class 2 fittings in which case there should be a sticker on the CU notifying of this I believe.
 

Reply to Zs Values. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
677
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
631
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock