you don't. Zs readings are dependet on the cpc. Zs= Ze+(R1+R2). you don't have an R2 so you can't measure Zs
 
Last edited:
either that or put N/A. don't forget to fix label on CU stating "NO CPC ON LIGHTING CIRCUIT" and note it on your cert. make sure that there are no metal fittings or switches. and that the switch pins screw into non-conductive lugs and don't bottom out on the back box .
 
Last edited:
It depends I take it your not installing it new, or adding to it as you wouldn't be able to with like that, so your doing a PIR in which case it would need to be marked down as a code deviation code 2 I think but maybe a 1 not to sure but defo a big bad deviation.

Unless none of the lights require a cpc class 2 fittings in which case there should be a sticker on the CU notifying of this I believe.
 

Reply to Zs Values. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
896
hello , can anyone reccomend a free download for max zs values for bs 3871 ct breakers please
Replies
2
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock