I've done hundreds and hundreds of loop tests on all kinds of circuits, and never had any problems of the kind your describing.

To be fair, i've IR'd Phase-Neutral on 500V by mistake more than a few times, and got away with it. Maybe I've been fortunate up until now!
 
There is no problem IR testing P-n but by joining P-N together on a PIR and testing to earth you're cutting out a step. As the book says P-N, P-PE, N-PE. If you do P/N-PE you only do one test as long as it all measures out ok (it should on a pir as it has been working for the last 75 years since the last one!!)
 
really? i've always done them seperately, way i take it, if you test P/N - PE, there could still be a dead short between Phase and Neutral and without doing the seperate tests you'd not know.

is this wrong?
 
If you are doing a pir then hopefully the breaker would have gone if there was a problem. On a new install check every circuit. but if the circuit has been in use since the dawn of time then a little discretion should be used. Testing is not just about taking a reading and writing it down but taking 5hitloads of readings writing them down, and then looking at them to see if they match up. Do everything by the book and you'll never be "wrong" but do it all with an understanding of WHY and it'll happen a lot quicker.
 
Fair comment. I suppose that's where competence plays it's part, there's a big difference in being able to think about things as compared to just doing things and going through the motions eh!

Hi All,
Connecting line & neutral together and tested to earth will not damage equipment during insulation resistance test.Never known damage to computers etc when left plugged in during loop test.


if you connect line and neutral, which jeremy has explained to me is perfectly reasonable, then it wouldn't harm any equipment plugged in because there would be no potential voltage to attract current from line to neutral. same theory as equipotential bonding

^^ does that sound about right?
 
Last edited by a moderator:
Spot on!! If P is 1GV and N is 1GV their potential difference is still a big ZERO so no current will flow ( between them, however at 1GV I wouldn't want to be in the same room!!!). I really hope this has helped with a bit of testing theory
 
hi all

then i have been lucky !!

tested zs at sockets with kit plugged in could not power down various reasons
obiviously no ir tests done

cheers

will think about this in future though
 
My 1653 doesn't have an isolation resistant tester. What should I do? And I don't understand the 1000V setting. Please help. yours expectantly, Jeremy.
 
A loop tester will test the earth loop impedance, it does this by inserting a resistor across line & earth, it cannot damage any other equipment connected to that circuit.
 

Reply to Zs in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
831
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
488
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5 MCB’S are 60898 what Max Zs would you put in...
Replies
31
Views
1K
Hi All, Any help would be greatly appreciated. When calculating the Zs for a circuit specifically for 2396 do you have to incorporate the on site...
Replies
1
Views
541

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock