Discuss I finished a job months ago , now the customer says somethings not working. Do I charge ? in the UK Electrical Forum area at ElectriciansForums.net
As above, just think about it, if it is some thing out of our control, then charge for it.So a few months back I fitted an outside socket , the customer has messaged me saying it doesn’t work and I need to come and fix it etc. do I charge ? As it was all working fine when I left.
But you worked on it....might have to suck this one up ?So after a conversation, it seems as if the connections have come loose. Basically it’s an outside socket that’s spurred from an existing outside socket. The furthest one (which I installed) is working however the one which was existing which I spurred from is not working.
Your connections in 'spurring' from it?it seems as if the connections have come loose.
So after a conversation, it seems as if the connections have come loose. Basically it’s an outside socket that’s spurred from an existing outside socket. The furthest one (which I installed) is working however the one which was existing which I spurred from is not working.
Thats the issue .Anything you directly touch becomes your responsibility . So in simple terms .... There is a 4 way wago connection and only 3 terminals are been used and you are then using the 4th . Its important to know the other 3 connections are GOOD . As any blame afterwards is going to be hard to fight . But we get paid for this so its not like we are doing something for free !So connections you worked on have become loose?
That's not good, that's very not good, personally I would be going back and putting it right free of charge as soon as possible.
I would be very upset knowing that a connection I made had failed and caused a fault. In the part of the industry I work in that kind of thing would very quickly damage my reputation and cause me all worlds of very expensive trouble.
And this is where arguments start between customer and electrician.The OP has already said its a loose connection so faulty socket/appliance is unlikely.
Presumably it was the customer has opened the socket to establish its a loose connection as the OP hasn't revisited yet?
I suspect the conductors whilst loose may still be touching one another, hence the other sockets still working.
But all hypothetical until OP re-visits!
exactly . The moment someone touches it...all bets are off. I did a job yonks and yonks ago. I knew it was perfect .1x months later I get a call saying part of it is not working .I turn up and ask if anyone has touched things .The visuals look fine, no breakers gone etc .Then 20 mins later one of the kids mentions that "dad did something and there was a bang " !!! turned out he had gone into the loft to add a TV aerial booster and had done the old twist and wrap in tape thing and not done it well . He looked very unhappy as he was charged the call out . I hate people that just cannot just be honestAnd this is where arguments start between customer and electrician.
I certainly wouldn’t be happy if someone else tried a repair a fault then said it was my fault…. Especially not an untrained customer.
That comes down to “well, who touched it last?”
I would hope the customer would contact me first to say it wasn’t working, I would go through the simple steps over the phone, such as checking the breaker…. Then advise them to turn off the circuit until I could go to it.
absolutely,exactly . The moment someone touches it...all bets are off. I did a job yonks and yonks ago. I knew it was perfect .1x months later I get a call saying part of it is not working .I turn up and ask if anyone has touched things .The visuals look fine, no breakers gone etc .Then 20 mins later one of the kids mentions that "dad did something and there was a bang " !!! turned out he had gone into the loft to add a TV aerial booster and had done the old twist and wrap in tape thing and not done it well . He looked very unhappy as he was charged the call out . I hate people that just cannot just be honest
True ... being honest and accepting a mistake works both ways . But there has to be ground rules to cover time etc if its not your faultTwo comments:
1) At this point even I’ll go and drive to the customer to tighten three bodged terminals for free just to shut this embarrassing thread!!
2) Picking up on what James’ said - it’s all about trust and honesty. Last year I had a phone call from a partial rewire I’d done, maybe two weeks after completion to say that the lighting cct was tripping. Thought it sounded odd as it had all been mint when finished and the job was a 2hr drive each way. Got there and instantly had that gut feel that something was off… half an hour of diags later and I discovered that old classic of the plate screw biting into the conductor after the customer had lifted the switch off for painting. He was mortified at having made such a clumsy error and thinking it was me, insisted I charged him a full day AND he bought lunch at the pub. But that’s not the moral - the point is that had I taken the defensive right from the start and said “no, not me” it could have led to a heap of grief AND me eventually having to attend anyway.
OP - just go and do it!!!
I play them along....Switches with the ability to change form, cables which move between terminals of their own volition - at least this must be what happens as everything has always worked fine until the day before. I like to gently break the news to these customers that no information could mean a lengthy fault finding processs, wheras small nuggets of information might just shave an hour or two off the bill and have me out the door in half an hour. Maybe I'm old fashioned, but I don't warm to people who can look me in the eye and tell bare faced lies.
Switches with the ability to change form, cables which move between terminals of their own volition - at least this must be what happens as everything has always worked fine until the day before. I like to gently break the news to these customers that no information could mean a lengthy fault finding processs, wheras small nuggets of information might just shave an hour or two off the bill and have me out the door in half an hour. Maybe I'm old fashioned, but I don't warm to people who can look me in the eye and tell bare faced lies.
Too far back in time to remember the specifics but I did one time find a note to that effect that just said "good luck!"I seem to get called in to fault find in houses that swear they haven't had any electrical work in 20 years, I can see the new MCB box rubbish dumped on top of the CU and some suspiciously shiny wago's for being 20 years old. Why lie? if anything it's a clue to past fiddling like a log book is for a car.
We should leave coded messages for future electricians by the CU, like client will follow you around like a sheep, or spaghetti nightmare escape immediately,