I'm wanting to add a couple of sockets in my caravan as there's only 2 at the minute. Not something I've ever worked on before, I'm going to have a flick through the regs just now but anything to be aware of?
One of the sockets is going under the bed (this area is accessible from the outside by...
hightower
Thread
caravan
electricians vans
electrics
fixed
still
van
vehicle
hi I'm a part qualified electrician gaining exp wherever I can whilst doing my college course.
Today we were hooking up a static caravan with 3 core swa. All was good until we started doing the tests. With the pme connected I was getting 0.26 as an earth loop at the board in the van. The boss...
Andy Barton
Thread
caravan
electricians vans
outbuilding
pme
van
vehicle
We stayed in a caravan in the last few days which had this fixed air blown heater underneath a wardrobe.
Inside the wardrobe the heater has a 13A mains plug with a PAT test sticker from 2012.
The switch on the front has been broken off and somebody has put in a block connected internally so...
logik1
Thread
caravan
electricians vans
fixed
heater
pat
pat testing
plug
tested
van
vehicle
Hi Guys
I'm doing an EICR and making expansion proposals for a Caravan Site. This is for holiday not static caravans.
Simple question - how many 16 amp outlets can I have off a 63 Amp supply?
Currently 8 pitches are fed from a DB containing individual 16 Amp RCBOs, fed from a 63 amp supply...
Piratepete
Thread
caravan
diversity
electricians vans
guide
site plan
supply
van
vehicle
Hi, looking for some advice for supply to static permanent caravan at bottom of garden.
My House supply is TT. From what I can gather from previous thread s, is this acceptable.
House end, SWA terminated into plastic ad.box and l+n tails into non RCD side of cu, from suitably rated MCB. Armour...
Has anyone been involved with the installation of a disabled alarm in a building remote from a occupied building.
I'm carrying out electrical works to a remote shower block in a caravan park,as an after thought the owner has decided to install a disabled toilet/wet room in the block.
He has...
My question is not quite in the title.
I've been asked to quote for the above. No extraneous conductive parts in garage, which I intend to supply from spare way in house domestic CU, swa to garage CU utilizing the earthing facility of TN-C-S.
However, one of the reasons they want the supply...
Hiya all
What we have is a holiday home site type effort where there are 13 caravan type looking units of accommodation.
They do not have towing facilities nor are wired for running lights while towing.
They are sat on wind down legs for adjustment.
Mobile Home - A transportable leisure...
Adrian Sadler
Thread
caravan
earth
electricians vans
home
homes
mobile
van
vehicle
Looking for a bit of guidance and how people go about connecting caravan pitches. Basically there is a PME supply on site which will be used to supply the toilet block and septic tank etc but I'm looking for guidance on how to terminate the hookups. There is a 16mm 3core armour run out to feed 3...
Hi All,
I've got a job to do at new caravan site. The client is paying for 3phase off of the pole that runs through the field and they have built a small solid building at the base. I'm assuming it's going to be connected as PME but i'm yet to confirm.
The client wants supplies to 5 pitches...
eddiecme
Thread
caravan
electricians vans
new
site plan
van
vehicle
Hi everyone,
The problem's history: Bought the caravan with an low level charged battery, hooked it to the main, heater and water pump worked for two days until the battery died. Bought a medium level charged battery, plugged it in and after three days it died. We checked the charger with a...
Delina Dimova
Thread
battery
caravan
charger
circuit
electrical work
electricians vans
mains
not working
static
van
vehicle
working
Hi all,
Got a look at a job today in a traveling site, we are installing a supply to a static caravan! The supply is tncs to a metal clad d/b in an out house,all circuits have rcbo protection!! There is a 100a rcd fitted,fed from the main isolator switch then feeding the d/b!! My ? is obviously...
I have a mate with a towing caravan battery charger problem. Scenario is the original fixed charger failed while he was away and he replaced it with a new straight swap unit...(3 stage 18a max unit). The battery is a 110ah unit which takes a charge fine on a separate trickle charger.
The issue...
I'm looking at placing a static caravan in my garden for elderly relatives to live in.
I already have a SWA cable from the house fusebox to the garage fusebox, and the static caravan would be situated adjacent to the garage.
Typically these caravans are connected to a 16Amp supply, will this...
smithgt
Thread
caravan
electricians vans
home
static
supply
van
vehicle
Hiya
Anyone know whats the minimum size for cable is for...
A. Cu to rod
B. Gas/water/chassis bonding
also if metal framework of the door need extratous bonding?
Cheers
Hello friends,
i have been doing EICR for caravan sometimes now. On 16A or 32A hookup box with 30maRCD protection mostly found 1ohms or more Zs at hookup and more inside the van. When you put the results in schedule of test sheet which will not comply with maximum Zs value table from regs book...
Hi guys been asked to install some meters on static caravans today. When checking it out I found the homes are all fed from the same supply with a weatherproof enclosure below each one where the SWA is connected to t+e that feeds each van. Should these not have their each individual hook up...
jimjamjimajam
Thread
caravan
electricians vans
static
supply
van
vehicle
Hi
I have started testing on a large caravan site i did a condition report and full inspection and testing on one caravan took me 3 hours.
The previous contractor (Niceic domestic installer ) does 10 caravans total of two people in 4-5 hours including certificates
My client has now asked me...
pmasouthwestltd
Thread
caravan
condition
cowboy
electricians vans
help!
never
sparky
test
van
vehicle
Hi
I have started testing on a large caravan site i did a condition report and full inspection and testing on one caravan took me 3 hours.
The previous contractor (Niceic domestic installer ) does 10 caravans total of two people in 4-5 hours including certificates
My client has now asked me...
pmasouthwestltd
Thread
caravan
condition
customer
electricians vans
site plan
static
testing
van
vehicle
wants