i need your help please this question is going to be a long 1...
first let me explain the situation...
Electrical Supply
The electrical supply to the house is 230V, 50Hz, single phase and together with the installation forms part of a TN-C-S system. The electrical intake position is housed in...
Have a job where Ze is 0.36 ohms on a TNC-S with 80A BS1361 suppliers fuse. The general rule, as per OSG (page 11), is if Ze is below 0.35 ohms then this is acceptable, but that relates to a 100A fuse (OSG fig 2.1 on page 15 refers). Now I believe that this installation should comply, so have...
Hi guys. In a week or so I have a oven thats in need of a new cupboard/unit that houses it. The plan is to isolate securely, disconnect, inspect/test the supply, and assuming all goes well to this point, fit the new cupboard/unit and then refit and reconnect the oven, MWC. Everything is going...
Just a quickie to refresh my memory.
TN system disconnection times.
Final circuits not exceeding 32 Amps.
230V 0.4 seconds. (table 41.1 page 46 BRB)
Final circuits exceeding 32 Amps IE fixed equipment and distribution circuits.
230V 5 seconds.
RCD's are used for socket outlets not exceeding...
Hello all.
Could any experienced sparkies please please explain to me how RCD tripping times can be adhered to when a PV sytem is integrated into a domestic consumer unit if the inverter takes up to 5 seconds to isolate the AC outputwhich it feed to the domestic supply at the consumer unit. Fed...
HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A
Anyone enlighten me, i need it for a 50A and 40A circuit??
thanks
Welchyboy
Thread
32a
circuit
circuits
disconnection
loop
max
reading
this slightly confuses me;
whenever a Zs reading comes up too high, e.g on a particularly long run, to get around the problem if you cant change the MCB rating, I get told to change it for an RCBO.
Table 41.3 of the regs gives max Zs values for both MCB and RCBO protection. If our Zs value...
Hi folks, client has requested PIR on a property with disconnected supply (not sure how disconnection has been effected). Property has been empty for a long time and potential buyer (retired electrician - no pressure) wants to know as much as possible to see if price can be negotiated down...
SW1970
Thread
disconnected
disconnection
earth
pir
property
supply
testing
tests
I'm looking at remedials from a PIR and one thing is a switch fuse with an 80 amp BS88 is serving a 16mm run of 2 core and armour SWA which serves 3 sub boards in 3 seperate outbuildings and they have been wired so they loop in and out at henley blocks until the final sub board. The total run is...
cadspark
Thread
boards
circuit
disconnection
distribution
final
probably
supplementary
time
This might help a few of us suffering the 2391 exam.
Maximum disconnection times for a nominal rms line voltage to earth, U0 of 230V
Firstly for a TN system:
Final circuits not exceeding 32A = 0.4s
Final circuits exceeding 32A = 5s
Distribution circuits = 5s
For a TT system
Final circuits...
hi there does anyone knowthe tripping times for a m.k.sentry 63 amp/2 pole/30mA r.c.d.device,it is part of a 8 way m.k.consumer unit,i am not sure if this device as a time delay incorparated,the number on the front of it is say's m.k.sentry /63 amp/5760s,your help would be appreicated,cheers...
Guys
BS 7671 table 41.1 shows that a disconnection time of 0.4 secs for 120<volts to <inc 230 volts, and a disconnection time of 0.2 at 230< to < inc 400v. (TN systems).
My query is with a 10%+/- tolerance which could possibly increase 230 volts to 253 volts hence taking your 230v 0.4s disc...
Hi guys ths is my first time on here and relatively new to electrics. I was asked to find the times of disconnection needed for 5x and 1x. I was wondeering if anyone could give me a push in the right direction by pointing out where i could find such useful info inthe BS 7671 or onsite guide...
volers
Thread
30ma
aus
circuits
current
disconnectiondisconnection times
guide
inspection
rcd
testing
times
within
Can a Sunnyboy SB3800 inverter disconnect on a TT system fast enough to prevent injury through shock?
The installation has an RCD fitted and the inverter is connected to a 16 amp MCB.
With the inverter having simple separation, does this negate the need for an RCD to protect the cable...
hi lads i have few questions: what is max disconnection time for site hut lighting on a construction site ?
max disconnection time for 110 V reduced low-voltage system ?
reasons for the use of a 20 mA RCD ?
Thanks for your fast reply!
Hi Guys,
Wonder if any of you could try and explain to me if the reason for disconnection times for fuses /proctective devices etc. As on one hand, i was told at college it is to protect the cable from catching fire etc, and then iget the impression the reason for having say 0.4 disconnection...
Hi I have a socket Radial off a 20A MCB and a lighting Radial off 6A MCB in a shed the board is fed by a 32amp MCB protected by an RCD on a TNCS syatem in the house. If I want the first point of fault ie the shed to trip first should I be using an RCBO for a TT system that trips under .2s? This...
Just
Thread
aus
cable
circuit
disconnection
house
installation
protected
shed
time
I've always wondered why BS7671 states that a disconnection time of 0.4s is required for circuits NOT exceeding 32A and for circuits exceeding 32A it is 5s
Surely you would want the higher current to trip quicker?
Can someone clarify this?
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.