disconnection

  1. W

    TT System and 30mA RCD tripping times

    Help! Sorry having a bad day. I understand the concept behind touch contact of 50v and the above 1666 ohms. But when physically testing with 17th ed dilog and testing a TT system 30mA RCD. At 1x and 5X what reading would you see on your meter? or would you just test the mechanical aspect...
  2. J

    Disconnection times

    Hello all I no the disconnection times for TN circuits are 0.4s for final ccts with an (in) not exceedind 32A AND 5 s for final circuits exceeding 32A Distrubution ccts I have just installated some lights within a industrial building in a riser and have tested all came back ok just have...
  3. T

    Disconnection Times

    Hi all, Just got a query regarding what values to use from the Red Book 32a Ring Main Domestic Circuit. Do I use the 0.4s Disconnection times or the 5s Disconnection times? regards Tom
  4. J

    Disconnection Times

    Am l right in thinking that its 0.4 seconds for under 32A and upto 5 seconds for anything 32A and above? If so why is that? :confused:
  5. S

    PIR Question

    My uncle wants his property tested as theres a new tennant going to be moving in and just by looking at it i can see its only his sockets that have rcd protection, shower etc don't. What code does this go down as on test sheet and do they have to be changed so that all circuits are rcd...
  6. S

    Part P Assessment ... disconnection time of an S Type Circuit Breaker w/ timed relay.

    Just had my Part P Assessment (and passed!) :) Although I was asked one question particulat question ... so Stuart, whats the disconnection time of an S Type Circuit Breaker with timed relay. My jaw and other parts of my body hit the floor! Funny thing is after I tried for 5 mins, he couldnt...
  7. O

    Help with PIR

    Hi Needing help with a PIR. 1. Old wylex type 2 CBs what BS is this an what Ka rating does it have. 2. MEM Memway 3 phase DB with rewireable fuses i take it they are a BS3036 3.The Memway is fed via an 60A TPN switch fuse Oterail make would this have a BS No 4. Method of protection on PIR...
  8. D

    Cooker Disconnection Time

    Cooker 30A I assume the disconnection time is 0.4 seconds, even though the outlet does not have a socket. Only circuits for distribution above 32A are 5 sec. Ta New comer:)
  9. H

    Is there any point testing earth loop impedance

    In a tt system? The earth spike is Reading greater than 50 ohms so clearly the mcbs won't make their rated disconnection times. Waste of time?
  10. albi

    315amp fuse max Zs

    does any one know the max Zs permitted for a 315Amp BS88 fuse got brain freeze know on page 45 of periodic report :mad:
  11. A

    16th Edition and RCDs?

    Can anyone give me a quick answer on whether or not the 16th Edition permitted the non-use of RCDs for additional protection? I've just had a call from a woman buying a house and she's described the consumer unit as having one rcd protecting cooker, shower and two socket circuits, but three...
  12. P

    schedule of inspections/supplementary bonding

    On page 3 of schedule of inspections (where you put a tick, X or N/A in the boxes), presence of supplementary bonding conductors appears twice - once in fault protection 1) automatic disconnection of supply and again near the bottom of the page under Additional protection. Have looked in the...
  13. P

    Domestic

    Guys don't have my big read book handy at mo can you answer the following 1. 32amp circuit were protective measure against electric shock is ads is the maximum disconnection time permitted by bs 7671 = 0.5s 2. maximum Zs permitted by bs7671 for a 32amp circuit 3. What is the bs(en)...
  14. W

    disconnection

    when filling in test sheets can you still put eebads or do you use ados
  15. D

    disconnection times

    would someone please explain the reasons for having a 0.4 second disconnection time and a 5 second disconnection time, why is there a big difference between the two readings :confused:
  16. P

    disconnection times

    guys, don't have my regs book handy at mo disconnection time for a tns system is 0.4 sec is'nt it
  17. scotsparky

    Max Zs for sub mains

    Anybody know where the chart for a BSEN 60947-2 Btype mcb are in the BRB?
  18. K

    Testing tt system

    Hi guys did a perodic test on a house today, was a tt system, all readings were coming back 493 ohms to 503 ohms which seems a little high to me. however max zs on tt systems on various mcb is not in the regs book, so what do you guys put in for you max zs??? do the above reading seem high...
  19. E

    disconnection time permitted for protective devices?

    what is the disconnection time of the protective devices protecting : a) a socket outlet circuit b) a fixed water heater circuit?
  20. michaelw6

    REF LINKS firstly for max disconnection times.

    Im always every night of every day of every week, on my pc doing my head in QUOTES. But on this occasion im actually doing an minor works. One thing that i never have on me at home is my onsite guide or regs book so id like to know if anyone knows any links to various places for info... First...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock