Evening All,
Is there anyone that knows what tests are required when carrying out injection tests on a Crompton Thermal motor overload type CR 12 /13 model.
Thanks
Sparky 63
Hi
I'm due to get my kitchen replaced and will be installing x2 2400w plinth heaters so will I require a seperate circuit or can I connect them to my ring circuit ?
FaLcO_1_
Thread
circuit
heaters
heating
kitchen
overload
ring
ring circuit
Hi
has anyone recently done the am2? I just wanted a basic calculation for setting the overload (they give you motor rating in Kw) for the 3 phase dol motor. I have tried looking this up for last few nights, but keep getting inconsistent or over complicated findings.
and people at work say...
Holiday let sleeping 8+. Gas ch (combi) and cooking. 2 x Wylex rewireable cu's, pme (6mm earthing conductor!), no rcd protection. 16mm dno supply, prob 100A dno fuse, no rating on meter but likely to be 80A
1 x cu for normal (lights, rfc's) etc. 2nd cu 60A rating with 3 x 45A fuses feeding 3 x...
I have an issue with a three phase submersible pump. The pump is controlled via a 55v control panel. The panel consists of the mains isolator, the 240 - 55v transformer for the control circuit, relay, contactor and overload. The pump works off three floats, one start one stop and one high level...
a big hotel group has asked us that they want 2 way dbs in each bedroom feeding one socket and 5 lights all led fittings, but they want the supplies to boards daisy chained from 10mm t&e or swa feeding 4 rooms per circuit. the only way ive ever done this is sub per board, but cant find anything...
Hi,
I'm an apprentice electrican. Please could someone give me some guidance on this as I am confused? Thanks.
What is the difference between overload rating ie 6amp on a circuit breaker and breaking capacity on a circuit breaker ie 10ka?
I'm confused.
Thanks
:)
Hi.
I am new to D.O.L but have sussed them out except I have one scenario I still need help with.
There is a single phase pool pump which is set to come on with a honeywell single channel 7 day time clock.
I have wired the D.O.L as single phase with a 230V coil.
The problem is I need the...
owenskinner
Thread
button
circuit
clock
contacts
overload
still
timer
Hello. I need advice about choosing MCB for cable overload protection.
I'm using BS7671:2008 Requirements for Electrical Installations.
Reg 433.1.1 has 3 requirements:
1. Ib <= In
2. In <= Iz
3. 1.45Iz >= I2
I don't understand reason of 1.45Iz >= I2.
And I think this requirements are...
Hi,
Just came across something earlier that made the have a think.
Distribution panel fed by 25mm cable.
This goes directly in to a D50 breaker.
The D50 feeds 4 6mm cables squeezed in top of the MCB that feeds small 3 phase bus bars, these in turn feed 1.5mm circuits.
I have fitted MCBs to...
Inteificio
Thread
breakers
cable
cables
distribution
inside
overload
panel
Hi all,
Could some one explain the correct way in connecting a 3phase contactor with overload protection.
I have the supply going into l1, l2, l3 and motor connected to the load terminals, t1, t2, t3. I also have the 230v connected to the a1 coil and neutral on a2. Just a bit confused...
Akanami
Thread
3 phase
contactor
current
motor
motors
overload
phase
hi guys if installing a shower consumer unit with a 63amp rcd main switch and a 100 amp OPD PRIMARY SUPPLY then main switch is of a lesser value than the main over current protective device how do we get around this.
foghorn
Thread
circuit
current
main
main switch
nominal
overload
rating
rcd's
shower
switch
Right following on from my last post.
i rewired a pizza oven circuit as the oven was being moved.its done in 16mm twin and earth.protected by a 50 a mcb.
guynfoned tonight saying after half an hour the circuit tripped so went up the oven is 13 kw can this be an overload?should I put a 63a mcb...
Hi guys in installing a 16mm submain with a 10mm earth and I'm going to install a 80amp time delay RCD with a 63amp MCB to protect it. Some one said I could just use a 63amp RCD to protect it? Never done this before and wouldn't think you could.
Also should I just use a 63amp RCD with a 63amp MCB
Hello,
I am an IT Tech and not an Electrician so please excuse my ignorance... I have three monitors, one 860W computer and multiple other devices including printers etc.. plugged into 2 x 7 UK Power Socket Extension Cords which can be found by googling the following: Belkin Conserve Smart AV...
AaronHatton
Thread
computer
equipment
overload
plugged
power
socket
sockets
wall
Hi Guys I hve a ring main that keeps tripping, but it also trips the main rcd on the board, is there a possibility that it is being overloaded? There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring of 10 sockets! Should the ring be...
Been reading various threads with regards to having an mcb that exceeds the cable rating thus only providing short circuit protection, what surprises me is the negative responses that are posted if it is ever suggested.
Now lets try put a translation on the regulation specifically 433-3-1 (ii)...
I'm probably going to get shot for this question, but when wiring a contactor/ overload does it matter wich side the supply is connected? I.E into the overload first or into the contactor and out through the overload?
I'm part qualified so you'll have to forgive my tiny brain...
12 x 50w Gu10s that have munched a couple of dimmers.(a silly load for a room that's abut 8 Msq)
I understand that with these halogens I may have to de rate the dimmer which would mean a 1200 watt dimmer (a bit pricy by the looks...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.