I was having a debate with my spark today about methods of joining above ground 3 core (E,L,N) 25mm SWA cable. We need to move the consumer unit and with it the meter tails (fused to 80A). This requires an extension of the tails as it is not possible to completely re-run them.
He said that the...
Good evening,
I was wondering if anyone has seen SWA cleats that would comply with the 18th edition reg 521.10.202 (i.e. not liable to premature collapse etc...)?
The data sheet for cleats produced by SWAonline say they are 'stable' between -350c and 1050c but they are still made of plastic...
Doing new supplies for a school new Shneider 3 phase & N MCCB panel board. 50mm 4 core SWA one end made off in the board earth fly lead from banjo to earth terminal. The other end gland made off in gland (fly lead not made off yet) 3 phases and neutral just hanging there. Done installation...
Toneyz
Thread
cable
insulation
insulation resistance
insulation resistance test
length
resistance
swa
test
Hi
I’m new to the forum & just a DIY’er!
I’m running a 15m length of 2.5mm 3 core (twin & earth) SWA to our decking at the back of the garden for a double socket.
Must the steel wire armour be earthed using the banjo or is the CPC core sufficient?
Thanks in advance!
J
Gents
I need to run 10mm SWA to building at the end of the garden, the electrician suggests clipping it direct to the fence concrete post which are solid enough and says is permissable as digging a trench is not an option. I am concerned about the UV issue, the support element as the posts are...
How long does 6mm SWA last before the sheath degrades if buried direct?
What would be the best ducting to run up a garden to a shed if ducting is needed?
plan to install a 70mm swa into a 3 phase board.
my idea is to install a schneider acti 9, 3 phase board, with standard incomer etc, and install a schneider extension box below it. incomer or mcbs will only take say 25mm, so planning on using the extension box to reduce the 70mm swa down to say...
At the origin the installation is TT.
Plan is to install a submain to a new db. Not carried out all the calcs yet, but my question is does the swa require an earth conductor in the cable.
Basically planning on running a phase and neutral or perhaps even 2 x phases and neutral.(the cable will be...
Hello all,
Just after some guidance, i am a qualified Auto Electrician with a good number of years behind me. While confident in my own ability in domestic applications i am not fully aware of the Regs.
I am planning on installing 3 or 4 (mind not made up yet) brick lights in my garden wall...
Looked at a job for a old boy- and wanted to keep costs down for him and make my job bit neater/simplier
Job is to get new swa from new little rcbo board inside house to a external ip65 light switch and then into 6x external lights
then he also wants to power his little shed at end of garden...
Hi all
I am after some help/Advice if possible please
A SWA sub main Distribution circuit has been given a Code 2 Rating on a recent EICR due to a high Zs of 2.8 ohms. The cable is 180 metres long and runs underground in ducting.
The Install is from a few years ago when a new Substation was put...
I have run 6mm t and e through the house from the db in the garage on a 32 amp mcb which is rcd protected. the 6 mm cable then goes into the back of an ip66 rated JB on the side of the house. i then intend to run 2 core (live and neutral) 6mm swa up to a workshop using the armour as earth.
my...
Hello All
Just a quick one does a three phase 25mm sub main in swa 4 meters long have to be fused even thou it comes from a bs1361 100amp services fuse then from a standard three phase isolation switch fitted from electricity company? Being swa and 25mm in size would this be acceptable? Reason...
Just installed a 70 mm 4 core Swa,height 5m on existing ladder rack.
120m,straight run with 90° turn.
Struggled with what we had but it’s in.
Just wondering have you guys ever used a cable winch to actually pull in a cable like this,is it easier ?
Also what labour would you have,& how many...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.