Discuss 0.00 ohms r1+r2 on radial circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Although technically its R1+R2 for your radial circuits. Whereas you record r1+r2 around your RFC with the highest value being classed as R1+R2. Is this a play on the capital 'R' telectrix?

no. with a rfc, you measure end/end of each conductor. these values are denoted by lower case r. when you cross connect on a RFC, or just connect L-E on a radial, you then measure R1+R2. ( denoted by upper case R ).
 
Quick quiz for you

A RFC has continuity values of r1=0.4 ohms, rn=0.4 ohms and r2=0.4 ohms

What is r1+r2?
What is R1+R2?

Ok. Here it goes. I would take r1 (0.4) and r2 (0.4) add them together (0.8) and then divide by 4 (=0.2). This would be the reading I would expect for all outlets within the ring main. So I test and I test, and test some more jotting down all my values as r1+r2. As I test, I notice I have what I think is a spur as the value is greatest and is actually 0.36ohms. This value being the greatest of the circuit is recorded as my R1+R2 for the ring circuit. PS: with the values you gave, I'm guessing the cables used are singles. Did I Pass?
 
it also stands for Rugby Football Club, but i wouldn't like to attempt an IR test on a prop forward.
 
Ok. Here it goes. I would take r1 (0.4) and r2 (0.4) add them together (0.8) and then divide by 4 (=0.2). This would be the reading I would expect for all outlets within the ring main. So I test and I test, and test some more jotting down all my values as r1+r2. As I test, I notice I have what I think is a spur as the value is greatest and is actually 0.36ohms. This value being the greatest of the circuit is recorded as my R1+R2 for the ring circuit. PS: with the values you gave, I'm guessing the cables used are singles. Did I Pass?

yes, but cable could also be SWA with the armour earthed but not used as cpc. the cpc core is the same size as the L and N.
 
no. with a rfc, you measure end/end of each conductor. these values are denoted by lower case r. when you cross connect on a RFC, or just connect L-E on a radial, you then measure R1+R2. ( denoted by upper case R ).
Slight hypocrite to note the importance of a capital letter when needed ....lol telectrix

Although I cannot say anything either ... but I didn't bring the subject up :):laugh3:
 
Slight hypocrite to note the importance of a capital letter when needed ....lol telectrix

Although I cannot say anything either ... but I didn't bring the subject up :):laugh3:

i blame it on my email addy which is all lower case.
 
you don't get that problem with a megger. can't deride flukes, though as i've never used one.
 

Reply to 0.00 ohms r1+r2 on radial circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi. I have a radial circuit supplying electricity to the garage (part of the house). It's on a 20amp breaker, uses 2.5mm cable. It currently only...
Replies
67
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock