Discuss 0.5A difference between 2 identical inputs. Solarriver 4000TL-D in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

I've done some tests with mine and I'm sure it's just the inverter displaying the wrong values.
It's been cloudless today so when the output was leveling out at its peak in mid afternoon I took 3 measurements.
1 Just string 1.
2 Just string 2.
3 both strings.

When I measured output at the generation meter (which I assume is properly calibrated) then String 1 gave 1756W (inverter read 1885W!), string 2 gave 1726W (inverter read 1728W) and together they gave 3420W.
So it looks like the inverter is reading high for string 1 but really both strings are giving out about the same power.
 
I have an indentical issue. A Samil Solar River 4000TL-D connected to 2x8 panel strings. PV1 always shows higher power output in all conditions by around 5%. installer diagnosed panels are OK by swapping inputs to inverter. New inverter arrived today so will see if there is a difference.
 
Was there a solution to this problem?
I'm on my 2nd Solar River 4000TL-D, both are reading consistantly low on PV2.
2 identical 2kw strings, due south facing - PV2 reads low even if strings are swapped round.
Low light (early morning and late evening) see PV2 reading around 45-50% lower than PV1, peak light sees around 10% lower.
Anyone got an answer?
 
Because this inverter is with 1 solar tracker their always will be difference between two strings. This is not really the ideal type of inverter.
The stronger string always will inject energy to weaker string.
You can use a string diodes to block this energy flow. I such cases better all panels to be in one string. (if it is OK with voltage at open circuit) .
High voltage - less current - less power loss, the other thing to be designed in that way.
 
Glad i found this thread, i noticed the exact same issue too.

4kW pv installed yesterday and i noticed string 2 performing around 0.5a less. The actual generation exceeded similar installs in the local area so i don't think there is any particularly wrong.

Have you concluded this is just an optimistic reading on string 1 or do we think the 2nd string is not a strong? Because it is cheap chinese kit? :)
 
A replacement Samil Solar River 4000TL-D was provided by Samil with firmware version 1.90 and the installer fitted it. The apparent difference between PV1 and PV2 output was still evident even when string swapped round so original inverter was refitted. Samil say they have a similar problem in Taunton and would get back to me. Have they?? No.
 
I'm on my 3rd inverter now and finally have one that is as close to working as I think I'm likely to get.

PV2 trails PV1 very slightly, but no where near as pronounced as the first two inverters.

This one is firmware V1.80 - the last one was V1.74, and the first one was V1.70.

Interestingly enough, the only firmware available of Samil's website is V1.70

I think it is string PV2 reading low, as opposed to PV1 reading high - simply because of startup and shutdown times. On my install, PV1 would "start" a good 45 minutes before PV2 and still be generating a good half an hour after PV2 had switched off..

This is my first day with inverter #3 so I'll post an update after a sunny day...
 

Reply to 0.5A difference between 2 identical inputs. Solarriver 4000TL-D in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi i have a 4kw samil power solar river inverter. when i log on it reading for pv1 shows zero for pv 2 i checked both strings with multimeter and...
Replies
3
Views
4K
F
A few weeks ago, I had my solar panels remove from my roof and then replaced. Sadly, on removal, one panel was warped and on letting the fixing...
Replies
1
Views
2K
R
Five days without solar but guess I haven’t missed too much yet, thanks to the grotty weather. I’ve had my solar installation since June 2011...
Replies
29
Views
4K
iconnect
I
G
Hi all I have just had a 3920KW Sharp 16 X 245W panels fitted with a Solar River SR4K4TLA1 inverter. There are 2 strings. One is currently...
Replies
30
Views
7K
garty611
G
L
I had 3.96Kw system installed along with a mastervolt K5500 inverter last November. We had various issues with performance and the system...
Replies
23
Views
4K
lennyg
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock