Why don't building site transformers have MCB's on the fly leads to what they are supplying?
Some do it seems, from the Blakley data sheet:

Overcurrent Protection
Input MCBs are Type “D” and output MCBs are Type “C”, to BS EN 60898.
All 32A sockets are individually protected by 32A DP MCBs.
Lighting circuits without RCD are protected by 10A or 16A DP MCB, as detailed above.


Taken from this product:
Their 4kVA one has a 16A DP input breaker, more in keeping with that sort of rating (unlike the 32A mentioned earlier in this thread).
 
Why don't building site transformers have MCB's on the fly leads to what they are supplying?
You have a thermal trip built into the transformer and over current protection and in the 13amp plug top.
larger kva transformer distribution feeding multiple equipment will have over current protection and mcbs on show on the side of the transformer
[automerge]1585905737[/automerge]
Like this type DA538F9E-1EE6-46C0-AF74-65E9668801A9.png
 
Last edited:
1.5kva only, not running anything fancy, only a vacuum and a biscuit jointer.
[automerge]1585906153[/automerge]
These are very basic questions for someone claiming to be an electrician

It's been eleven years since I retired and anywhere near a building site so have had to make room in my brain for other things.
 
1.5kva only, not running anything fancy, only a vacuum and a biscuit jointer.
[automerge]1585906153[/automerge]


It's been eleven years since I retired and anywhere near a building site so have had to make room in my brain for other things.

The basic principle of protecting circuits should still be there though surely?
 
It is showing a 10 way dist board with 16A type C protective devices. It doesn't indicate whether single or double-pole devices but it should be double-pole.
 
Last edited:

Reply to 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
847
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
717
Hi all, I've just installed an APC 6KVA SRT6KRMXLI. As a computer network engineer and electrician, I was a bit baffled by the 35mm gland that...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock