Discuss 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

It is showing a 10 way dist board with 16A type C protective devices. It doesn't indicate whether single or double-pole devices but it should be double-pole.

Oddly it is not showing MCB specified at the sockets, unless that is specified off-page or in the list of parts?

Certainly the ideal solution to me would be a board right next to the transformer (less than 3m cable) and all DP MCB there.
 
Oddly it is not showing MCB specified at the sockets, unless that is specified off-page or in the list of parts?

Certainly the ideal solution to me would be a board right next to the transformer (less than 3m cable) and all DP MCB there.
You don’t need mcbs at the socket positions if you have DP mcbs at the origin of the circuits
 
The spec is poorly worded indicating single-pole and neutral, it should say two-pole and earth.
 

Reply to 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
845
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
715
Hi all, I've just installed an APC 6KVA SRT6KRMXLI. As a computer network engineer and electrician, I was a bit baffled by the 35mm gland that...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock