hi there. Starting a job soon to install 2 6 way dis boards in outside cabinets. At the bottom of the hill there is a Scottish power main switch installed. I was wanting to run a swa from there to first cabinet then run another swa from cabinet to other cabinet. From SP to first cabinet the cable run is 100m and from 1st cabinet to 2nd cabinet cable run is 190m. Loading for each cabinet is 8kw each. Will this be ok to loop supply in some sort of joint box with appropriate connectors
Thanks
 
Too many unknown factors. You're asking for assumptions, although, for starters have you thought about the required cable size due to volt drop.
 
If I was designing this I would probably have over current protection for the second distribution circuit in the 1st cabinet. that's quite a load over 200 meters. Have you carried out any calculations?

Agree...if the connections will take the cable size with another 190m to run :wink:
 
I don't see a problem with more than one DB on a distribution circuit, subject to the usual cable calcs. Too many circuit breakers in series will lead to lack of discrimination in the event of a fault.
 
If I've understood correctly, probably 50mm cable which is over £1k per 100m. Well worth having a proper design done by an expert (not me :) )
 
If this was me, I would run a cable to cab1, install a small 100A bus bar chamber, then a switch fuse off this for the board in cab 1 and then a switch fuse for the Sub main up to cab 2.

What size cable have you calculated out of interest?
 
If this was me, I would run a cable to cab1, install a small 100A bus bar chamber, then a switch fuse off this for the board in cab 1 and then a switch fuse for the Sub main up to cab 2.

What size cable have you calculated out of interest?

You could run in to discrimination issues with that arrangement leading to the supply to the first cabinet being oversized unnecessarily.
 

Reply to 2 dis boards off one cable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm working on a site in the UK where a joinery company will be installing bespoke vanity cabinets. The cabinets will have MDF/mirrored doors with...
Replies
4
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
808
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock