Hi all, just looking for an outside opinion on this.

A collegue and I are going to be installing 4 three phase EV chargers on a site. He's of the opinion that we will need to invert the phase at each charger in order to balance the load, i dont believe this is correct as equipment with 3 phase input already pulls equally from each phase.

Whats correct here? Any advice appreciated.
 
As Brian above,

But you'd need to do some investigation first as the charger may have a setting to change the phase used for single phase charging,
or the chargers may be assembled with a random phase sequence to reduce the risk of all chargers being on the same phase for single phase use
or the charger may use a different phase each time it's used for single phase.

So by physically changing the phase to each charger you could potentially end up with them all on the same phase in single phase useage.
 
Hi all, just looking for an outside opinion on this.

A collegue and I are going to be installing 4 three phase EV chargers on a site. He's of the opinion that we will need to invert the phase at each charger in order to balance the load, i dont believe this is correct as equipment with 3 phase input already pulls equally from each phase.

Whats correct here? Any advice appreciated.
What’s the model number of the charging points your installing some are more capable at load sharing than others.
A good read of the manual/specs is always an option
 
Hi all, just looking for an outside opinion on this.

A collegue and I are going to be installing 4 three phase EV chargers on a site. He's of the opinion that we will need to invert the phase at each charger in order to balance the load, i dont believe this is correct as equipment with 3 phase input already pulls equally from each phase.

Whats correct here? Any advice appreciated.
On a EV charger course I did recently when connecting multiple 3 phase chargers it was recommended that the phases at each charger are rotated and each charger programmed with the connected sequence. This is because most vehicles will only charge on single phase from L1 the reason for programming the phase rotation on each charger is so the load management doesn't limit the charging on L1 at all the chargers because it believes the phases are in the normal sequence
 
On a EV charger course I did recently when connecting multiple 3 phase chargers it was recommended that the phases at each charger are rotated and each charger programmed with the connected sequence. This is because most vehicles will only charge on single phase from L1 the reason for programming the phase rotation on each charger is so the load management doesn't limit the charging on L1 at all the chargers because it believes the phases are in the normal sequence
Agreed, but that's as long as the load management supports phase optimization and can map the phases correctly.

Hence, why I asked the OP #5
 

Reply to 3 phase load balancing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What can be worse than electrical installations on a farm, or in a pub?...... Chippys! Got a phone call from my local.... Lights and kitchen...
Replies
6
Views
846
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
907
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello folks. I am about to complete on a (detached) house purchase and I want to ask your advice whether to have three phase connected to the...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock