Afternoon all,

Looking for a little guidance, other than doing sub mains in armoured I don’t do much three phase work.

I’m looking to install some final
Circuits for some three phase cooking equipment but I find myself stuck on a few things, as the sockets will be over 16amp they will need to be rcd protected but I can’t seem to find anything to find a Hager board rcbo etc. What’s the best way to protect it?

Also generally if doing a three phase sub main I would take an additional earth as I’m not so keen on solely relying on the armoured earth. Do most people generally rely on the armoured earth or use 5core?

Thanks for your help
 
I would do 1 of 2 things..
Don’t have the sockets protected by an RCD, subjust to a risk assessment or
Have the appliances hard wired into an isolator, negating the need for RCD protection, subject to installation methods.
You can have an RCD incomer protecting all circuits if necessary..
Have you done any adiabatics?
 
Also generally if doing a three phase sub main I would take an additional earth as I’m not so keen on solely relying on the armoured earth. Do most people generally rely on the armoured earth or use 5core?

Sockets with RCDs built in are usually more readily available and a simpler solution than three phase RCBO's, these are often made up from add on modules and quite big taking up 6 ways in a DB.

This mostly comes down to the quality of the glands you use and your ability to fit them correctly. If you fit the correct gland properly then there will be no problem.

If fitting standard surface mount commando sockets with the plastic threaded entry there is rarely room to fit an earth connection to the SWA gland. You may need an adaptable box or besa box to gland the SWA to and make the earth connection or use 5 core cable.
 
For earthing glands i am using earth lock nuts most of the time now.

An example -

WISKA EN20 P NUT 20mm brass locking earth nut PIRANHA - Edwardes - https://www.edwardes.co.uk/en/products/wiska-en20-p-nut-20mm-brass-locking-earth-nut-piranha?utm_medium=google_shopping&utm_source=google&utm_campaign=google_shopping&gclid=Cj0KCQjw-tXlBRDWARIsAGYQAmeN9Z9Jx_4XnSpqMDlLjwq56Hz4Pwu85dzG4rq9lTGRGB_FOPWeUIAaAtpaEALw_wcB

MCB in the board and RCD in the socket outlet is the standard way to do this i believe. Use a socket with a built in rotary isolator takes care of isolation as well.
 
New posts

Reply to 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
768
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
851
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
839
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
879
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock