Discuss 5 amp or 13amp for 1000 watt appliance in the UK Electrical Forum area at ElectriciansForums.net

Yaqub

-
Reaction score
8
Hi all,

Quick question hope someone can shed some light on.

I have a single coil burner with the following labelled specifications;

1000 Watt
220/230v
50/60hz

It comes fitted with a 13 amp fuse, but after reading a short bit about fuses I got the impression it might be too high.
The calculations I came across was 1000w/230v=4.34 and another 1000w/230v=4.34*1.25=5.43
Would a 5 or 10 amp be better suited?

Thank you
Yaqub
 
the 13A fuse is to protect the cable to the appliance, not the appliance itself, which is a fixed load, so if the cable is 1.5mm, the 13A fuse is correct. nothing to stop you downrating fuse if you want.
 
It seems to be a practice from some manufacturers these days to rate the cable for the appliance. For example a 2kw heater will have a 1.0 cable fitted which is rated at 10A but the fuse fitted is 13A. The theory being the nature of the fixed load will not exceed the ccc of the cable and hence the 13A fuse serves little purpose in respect to protecting the cable.
 
It seems to be a practice from some manufacturers these days to rate the cable for the appliance. For example a 2kw heater will have a 1.0 cable fitted which is rated at 10A but the fuse fitted is 13A. The theory being the nature of the fixed load will not exceed the ccc of the cable and hence the 13A fuse serves little purpose in respect to protecting the cable.
it will give fault protection but maybe not overload protection. either way, for a fixed load, it is compliant.
 
What would be the solution for an identical model but with a German plug?
I bought it and never bothered returning it, so thought to add on a adaptor and start using it. Not sure on fuse for that either though.
 

Reply to 5 amp or 13amp for 1000 watt appliance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
461
Hi Quick question, I have the following appliance lying around and wanted to make use of it, it comes with a German plug with the following...
Replies
23
Views
2K
Deleted member 26818
D
Hi all, I've recently ventured into hiring products and providing services for events/weddings etc. We've been at it for a couple of years now...
Replies
6
Views
1K
Hi, Our old oven was plugged into a standard socket behind the adjoining unit with a 13amp fuse standard plug, the hob has it's own isolator box...
Replies
9
Views
873
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
Replies
8
Views
6K
Specialist
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock