Discuss 50v on swa banjo ? TNC-S system new build in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I’ve had a weird one today. Banjo having 50v on it.

L - main earth = 230v
L - N = 230v
N - main earth = clear

I have 50v on the live - banjo & 24v on the Neutral - banjo.
Disconnected both sides of the armoured and done insulation resistance between all cables and all <999.
 
Have you done continuity tests on the SWA?
Where were your first and second test results carried out?
 
Surely the banjo is earthed if you are testing voltages to it, if you disconnected the earth to the banjo but the box or whatever its fitted to is screwed to a wall or something then you will still get some voltage between it and live.
 
L - main earth = 230v
L - N = 230v
N - main earth = clear

What does clear mean? Is that 0V between them or no continuity between them?
I have 50v on the live - banjo & 24v on the Neutral - banjo.

Does the banjo have fly-leads fitted or is it one of the all-too-common wireless ones?

Disconnected both sides of the armoured and done insulation resistance between all cables and all <999.

Did you test IR between the conductors and the armour?
 

Reply to 50v on swa banjo ? TNC-S system new build in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
762
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
709
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
528

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock