Discuss 6mm Main Bonding on TN-S domestic install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

how would you do it?

check no signs of thermal (or mechanical) damage do continuity test on conductor, check adiabatic Ze, Zs etc then make an informed decision.

this is not a get out of upgrading bonding clause and in my humble opinion it should be carried out when possible.

Also a mention that pme supply must be pre 1988 if existing bonding is to be left in situ to comply with electrical safety regs.

Looked into this as firm i worked for were replacing load of social housing consumer units but didnt want bonding replaced unless needed so wanted something a little more concrete than "my boss told me to do it"
 
Last edited by a moderator:
Adiabatic is not applicable to bonding conductors.
and as ezzie says, use adiabatic to determine required size of main earth, then bonding needs to be not less than 50% of that. (TNC-S notwithstanding)
 
I actually mentioned DOMESTIC in my original post question as this is what the question was refering to.

On a Domestic TN-C-S with a 16mm bonding to the MET, my bonding to Gas and Water services must be 10mm if not mechanically protected?
 
Last edited by a moderator:
show/hideQ12. When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?

Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.

Regulation number(s)
  • 132.16
  • 544.1.1
Just had similar problem ,researched into threads.The above para taken from the Electricity Saftey Council. Question and Answers page , Alterations.Would appreciate any ones take on this ??? hope there is no stoney silence!!!!!! i take it this refers to the main bonding
 
Last edited:
was hoping to find some answers when i searched for this but all i found is a bunch of gits flirting with each other...!!!?!?!?!?!?:willy_nilly:
 

Reply to 6mm Main Bonding on TN-S domestic install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
707
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
901
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock