Discuss A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Cheers for that, I hope I don't sound like an idiot, but at what point does the Zs change the choice of circuit breaker. It's a TT system by the way.
 
I think we are now entering the realms of competency here ....................... I will hand you over to my learned friends I think

You are not talking circuit breaker but RCD protection, but even if not then the type of circuit breaker is very relevant and is certainly linked with Zs values.
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.

That in itself is not a requirement for RCD protection of a distribution circuit.
 
Thanks, but some of us have been taught that the DNO will not accept that on a TNC-S system. I am not trying to be contentious here but wonder where that myth came from.
 
Thanks, but some of us have been taught that the DNO will not accept that on a TNC-S system. I am not trying to be contentious here but wonder where that myth came from.

From bias lectures that don't like PME earthing!! That seems to be one of the biggest influences anyway!! Same goes for RFC's, Using the Armour of SWA cables as the circuits CPC, and a few others too boot as well...lol!!
 
What another cracking thread. So in summary so I can go forward,

1) We can export if practicable, if not TT it with all the usual requirements.

2)If we do export then a 10mm Main bonding cable must be provided, if services enter the location

3) If the CSA of the supply cable is <10mm we must provide a separate Main bonding conductor of 10mm

4)If the supply cable CPC CSA is > 10mm or + we can use said CPC as our 10mm main bond


Have I missed anything ?

My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)
 
I have GN8 on back order from Amazon can't wait to get my nose in it..sad ain't i....
The was a time I would have a crumpled copy of Mayfair or Penthouse rammed down the back of the toilet systen..now it's electrical pawn lmao

ATB J
 
My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)

Yes, the main protective bonding conductors on a PME system are sized in accordance with the SUPPLIERS neutral conductor (not the tails) and as you rightly say, there is no provision to reduce the size in a distribution circuit to another building with main protective bonding requirements.
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 
New posts

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
417
I realise this is a much-discussed topic, I have certainly read a lot on the forums already! However I wish to ask about the subtitles of...
Replies
21
Views
5K
Thought this might be of interest and use to anyone looking to undertake the various short training courses. So here is my recent experience -...
Replies
11
Views
4K
Appreciate a bit of advice regarding this that I'm doing in the morning- Consumer unit upgrade in house with 6mm gas & water bonding existing...
Replies
63
Views
8K
baldsparkies
B
In the process of quoting and pricing a job for an outbuilding which is to be used to cut hair on a part time hobby. This outbuilding will have a...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock