Discuss A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Thanks IQ. But what if user is wearing wellies and there's no RCD protection in garage (but is in house). User is holding failed tool and therefore a live part, hasn't got a shock because there's no earth path but then touches water pipe on side of garage. Will MCB or RCD in the consumer unit in the house provide any protection? If no, then shouldn't earthing be improved in the garage (e.g. bonding of this pipe and either TT or 10mm2 back to consumer unit). Thanks, SW.
 
If there's RCD protection in the house and the garage is fed from the house...then the garage will be RCD protected.....it doesnt matter how far back up the system the rcd is...the current imbalance it see's will be the same.
 
Last edited by a moderator:
:wink5:
For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!

An important omission is the fixing height of a socket outlet in a garage.
The 17th Edition of the IEE Regs require it to be fixed at a suitable height.
The 13 Edition stated a height of 4ft 6 inches. (1.5 metres)

This was to try to remove the risk of explosion / fire from petrol fumes.
This is a good guide line for today's installers
 
Hi just a reply to the Thought that Neutral breakdowns in PME supplys are Rare,, Last week I was called to a house that had been recently rewired by another party and then tenants moved in..
Dueing the day they were shocked to see smoke from under kitchen sink. the flexy hose had melted and blown apart leaking water across the kitchen a plumber came out to fix it and got a shock everytime he tryed to reconect it, an electrician was called but couldnt find the problem!!
i was called and found a high resistance on the neutral supply and when the kettle was put on and the shower run (any high load) The main and supplementary bonding became the prefered return path!!! just a thought when running to external systems garages etc.. a nice metal framed garrage would make a lovley return path!!... also note this was a 17th edition board so completly RCD protected the RCD was never unbalanced because the fault was external of the RCD
 
Last edited by a moderator:
This subject has been done to death over on the S/F Sparks Forum.

A few years ago I posted what I called tongue in cheek thread about 'The Utimate PME/TNS Exportation'

The following is a Cut & Paste from said thread with suitable updates for the current Regs.

The Ultimate PME/TNS Exportation! by Sinewave.

Existing
PME/TNS supply at service position.


Run a minimum of 10mm 3 core SWA cable to your external location, following all approved cable installation
procedures.

Terminate in to a 17th Ed Metal Clad Dis-Brd or use RCBO's for all Circs depending on size of remote installation.

Link SWA Earthing Tag to DB-2's MET with 10mm, despite it being a Metal Clad Dis-Brd.
(Belts & Braces!)

Drop an Earth Rod in as close as possible to DB-2 and connect back to DB-2's MET with 10mm

Bond any metal services entering
the remote building with 10mm

Bond any exposed metal framework of the
building with 10mm


Resultant installation has an excellent Ze DB-2

Resultant installation is tied down to 'True Earth' at it's remote
location thus avoiding any 'potential' differentiation problems between the MET at the DNO service poistion/DB-1 and the remote installation at DB-2.


Most of the UK's MV Network is PME'd now lead or otherwise as all joints have a Rod dropped in as a matter of course.
 
The way i look at is, if i export PME am i taking it into a zone where an equal potential can be created. If it can then there's no more of a risk than anywhere else.

Personally if i cant create an equipotential zone i wont export, or ill go done the route of placing an electrode system of a suitable Ra to keep the touch voltage down.

With the country now becoming pretty much PME it will be interesting to see the rate of failures on the network to see how rare these broken pens are now.

Regards Chris
 
The way i look at is, if i export PME am i taking it into a zone where an equal potential can be created. If it can then there's no more of a risk than anywhere else.

Personally if i cant create an equipotential zone i wont export, or ill go done the route of placing an electrode system of a suitable Ra to keep the touch voltage down.

With the country now becoming pretty much PME it will be interesting to see the rate of failures on the network to see how rare these broken pens are now.

Regards Chris

And that's what it all boils down to....
 
The way i look at is, if i export PME am i taking it into a zone where an equal potential can be created. If it can then there's no more of a risk than anywhere else.

Personally if i cant create an equipotential zone i wont export, or ill go done the route of placing an electrode system of a suitable Ra to keep the touch voltage down.

With the country now becoming pretty much PME it will be interesting to see the rate of failures on the network to see how rare these broken pens are now.

Regards Chris

Why not take the PME to the outbuilding/shed or whatever, and connect a rod to the EMT at the small CU?? You then have best of both worlds relatively speaking. Personally i wouldn't feel the need to rod, i'd be more than happy with the PME...

The way things are in modern times, is profits Rule!!! and it's how much that maintaining PME is going to eat into those profits that will decide. That and substantial fines and/or damages for Not maintaining their LV network earthing systems...
 
Why not take the PME to the outbuilding/shed or whatever, and connect a rod to the EMT at the small CU?? You then have best of both worlds relatively speaking. Personally i wouldn't feel the need to rod, i'd be more than happy with the PME...

The way things are in modern times, is profits Rule!!! and it's how much that maintaining PME is going to eat into those profits that will decide. That and substantial fines and/or damages for Not maintaining their LV network earthing systems...

Well i think we are singing off the same hymn sheet, connecting an electrode system at the emt or met if at the correct Ra will maintain a safe touch voltage upon a broken pen, or do you mean take out the PME and the divorce the earth at entry?

Regards Chris
 
Well i think we are singing off the same hymn sheet, connecting an electrode system at the emt or met if at the correct Ra will maintain a safe touch voltage upon a broken pen, or do you mean take out the PME and the divorce the earth at entry?

Regards Chris

Come on Chris, why would i want to ditch a superior earth and replace it with a TT system!! ...lol!!!
As i said in my post above i wouldn't feel the need to add an earth electrode to the EMT of an outbuilding. But if there was an existing rod in place, near to the outbuilding, of course i'd certainly make use of it!!
 
Come on Chris, why would i want to ditch a superior earth and replace it with a TT system!! ...lol!!!
As i said in my post above i wouldn't feel the need to add an earth electrode to the EMT of an outbuilding. But if there was an existing rod in place, near to the outbuilding, of course i'd certainly make use of it!!

Lol, when i was replying i thought as much, just testing :).

Regards Chris
 
one thing this whole topic has made me think about is that when I happen to be taking a 10mm sub main or bigger to an out building I automatically have an earth wire large enough to cope with bonding, so or though I would normally make this area TT I could legitimately connect it to the PME incomer.
 
one thing this whole topic has made me think about is that when I happen to be taking a 10mm sub main or bigger to an out building I automatically have an earth wire large enough to cope with bonding, so or though I would normally make this area TT I could legitimately connect it to the PME incomer.
Yes if the CPC of the sub main is 10mm² copper, then it could be used as a bonding conductor.
The problem being that the armour of 10mm² SWA being steel, does not have an equivelant conductance to 10mm² copper.
Thsi leaves you with the choices of 2 core SWA and a rod, 2 core SWA and a separate bonding conductor or 3 core SWA.
 

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
436
I realise this is a much-discussed topic, I have certainly read a lot on the forums already! However I wish to ask about the subtitles of...
Replies
21
Views
5K
Thought this might be of interest and use to anyone looking to undertake the various short training courses. So here is my recent experience -...
Replies
11
Views
4K
Appreciate a bit of advice regarding this that I'm doing in the morning- Consumer unit upgrade in house with 6mm gas & water bonding existing...
Replies
63
Views
8K
baldsparkies
B
In the process of quoting and pricing a job for an outbuilding which is to be used to cut hair on a part time hobby. This outbuilding will have a...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock