Discuss Adding socket on to kitchen ring-no rcd in the UK Electrical Forum area at ElectriciansForums.net

Chris

-
Reaction score
26
Hi all,

I was asked today to add 2 extra sockets on to an existing kitchen ring, however the board is an old wylex with the push in MCBs so no rcd protection. To add the extra sockets would it require A board change/rcd isolater?

Thanks
 
You need to add RCD protection where it is required for sockets and possibly buried cables. How you achieve this is up to you and your customer's wishes/budget.
A separate RCD next to the board is a cost saving favourite.
did just that last week, £3 plastic enclosure, used a rcd left from a board upgrade where i installed rcbos. so no cost for the rcd. routed circuit via new enclosure next to board. can still use plastic enclosure for a rcd on its own so no need to spend the cash on a metal enclosure.
 
did just that last week, £3 plastic enclosure, used a rcd left from a board upgrade where i installed rcbos. so no cost for the rcd. routed circuit via new enclosure next to board. can still use plastic enclosure for a rcd on its own so no need to spend the cash on a metal enclosure.

So to do this, would you insert the RCD enclosure between the circuits mcb and 1 of the ring finals legs?
 
WYWRS32SLASH2.JPG
bang one of them in enclosure .
 
did just that last week, £3 plastic enclosure, used a rcd left from a board upgrade where i installed rcbos. so no cost for the rcd. routed circuit via new enclosure next to board. can still use plastic enclosure for a rcd on its own so no need to spend the cash on a metal enclosure.

You dont class an rcd as switchgear then? I dont agree with that you are complying with current regs in that scenario!
 
did just that last week, £3 plastic enclosure, used a rcd left from a board upgrade where i installed rcbos. so no cost for the rcd. routed circuit via new enclosure next to board. can still use plastic enclosure for a rcd on its own so no need to spend the cash on a metal enclosure.
Not for one minute putting any dispersion on your installation but doesn't it make a mockery of the regs when the enclosure can be plastic when you are installing the same switchgear?
 
You dont class an rcd as switchgear then? I dont agree with that you are complying with current regs in that scenario!
NICEIC tell me I can use plastic enclosure, i queried this in light of the 18th ed, response i got from the NICEIC tech support below

Although we would recommend it, generally any enclosure used solely for an RCD would not fall under BS EN 61439-3 and would therefore not require a non-combustible enclosure.
It is permissible to carry-out additions or alterations to an existing plastic enclosure consumer unit where the designer considers it adequate for the altered circumstances, there are no signs of thermal damage, product recalls and complies with the version of the regulations it was designed and installed to. Any planned change of the consumer unit would require a non-combustible enclosure.

We trust this answers your questions.


Hence why i have used a small plastic enclosure and put a RCD in and had no concerns. it was the most cost effective and simple option of adding RCD protection the the circuit i was working on. Otherwise it would have meant a board change. i was also quite limited in terms of space by the board so a small enclosure did the trick.
 
Not for one minute putting any dispersion on your installation but doesn't it make a mockery of the regs when the enclosure can be plastic when you are installing the same switchgear?
As above ^ The regulations are an enigma at times. It does seem strange that you can circumvent them in this way. Ultimately though the issue is one of attention to detail and workmanship, If you install the cables correctly and ensure they are terminated right then you should not get loose connections or thermal damage that cause issues of worse case a fire. the vast majority of the Cu fires that led to the changes to metal/non combustible were due to poor workman ship and people not checking screws, terminations etc...
 
Out of interest..
Do the regs at present apply only to CU enclosures? I'm thinking we have a portable machine with a plastic IP rated enclosure, which contains 3x RCD's and a 2-3 MCBs on each of them. This arrangement is because the incoming supply is 3 phase, and the phases split into each RCD then onwards via MCBs rated to the various single phase bits of kit they supply (pumps/motor valves/transformers etc).

If it does apply, when did this change happen roughly? The machine was designed about 5 years ago so not sure if it would be covered or not.

In case anyone was wondering why we went for the plastic enclosure, it's because our kit is often temporarily in damp areas or even outdoors in rain (normally not powered up but needs to be transported by HIAB truck, so not covered to protect from rain/road spray. I'm not sure I would trust a metal enclosure to sit in damp areas for weeks on end and then get sprayed with salty road water on the way back home... Might not last that long.
 
Reg 421.1.201 applies to domestic properties, thought you supplied electrical devices to that underwater dance thing?

Interesting guidance about the plastic RCD enclosure. The advice I got (Elecsa) a while back, was more unhelpfully vague. See if I can locate it.
 
You dont class an rcd as switchgear then? I dont agree with that you are complying with current regs in that scenario!
He didn't say it wasn't switchgear. That doesn't mean that it's a similar switchgear assembly to a distribution board though, which is what the Regulation actually states. It doesn't provide overcurrent protection so isn't similar.
 
He didn't say it wasn't switchgear. That doesn't mean that it's a similar switchgear assembly to a distribution board though, which is what the Regulation actually states. It doesn't provide overcurrent protection so isn't similar.

In fairness, me and a lot of others were of the same opinion, and the guidance I received went in a similar vein. To some the reg is clear as the days long, but IMO its not, and they have had the opportunity to make it clearer.

Doesn't make sense, that two pieces of similar equipment or enclosures can be installed side by side, one has to be metal the other doesn't.
 

Reply to Adding socket on to kitchen ring-no rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
692
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
670
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
290

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock