Discuss Advice needed on unconnected earth wire. in the UK Electrical Forum area at ElectriciansForums.net

If you don't know any sparky friends or family then you must bite the bullet and get a sparky out. Wouldn't be a lengthy job and you'll know you'll have a safe install once he susses what's what. As previously mentioned it looks like main earthing conductor protecting your property not connected.
You say you had new CU in 2016? If it is main earth and not a supplementary......go put the lotto on.
Please keep us updated.....
PS could you take wider screenshot photos as it might make more sense from a distance. It looks like your water is bonded but not your gas?
 
Wow, someones made a boo boo there
There are a ton of these around and for a long time as well - last one I did it wasn’t connected for 20 odd years and the earthing was via pipework bonding. Zs of 2.70 ohms with bonding going down to 0.24 or so when simply connected!
Agree though that you do need to call the same spark if possible and see the shade of red on their face.
As Pete picked up though, that earth braid looks sparkling new so maybe some DNO work but as Littlespark came back - that earth conductor end has never been squeezed!
As Toyah once sang “it’stha mysthery oh it’stha mysthery”!
Looks as though that braid goes to that Henley block which it makes even easier for a connection and test.
 
20190425_140142.jpg


seems this is common. I got called out last week and asked if this was normal by a couple who selling a relatives house. the new meter was put in a few years ago. must be a new type of wireless earth connection as well
 
earthing systems are complex with many variables involved,
not to mention lots of rules and regulations,
don't guess or take anything for granted,
get a proper electrician in to check everything
in relation to your earthing,
that way you can be ensured it is safe and code worthy.
 

Reply to Advice needed on unconnected earth wire. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
921
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
737
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
353
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock