The buyers of our flat (upper floor of a two flat building) have just had an EICR done and it has flagged a number of C1’s and C2’s. I was hoping someone might be able to give a second opinion as to whether the C1’s listed are reasonable (ie should they be C1’s). I’m no expert (at all) and if they are reasonable then fair enough, but would be great if anyone is able to give a second opinion.

-Main earth extremly high at origin - C1
- All downlights are not fire rated - C2
  • No CPC conection through downlights - C1
  • Lights wired in 1mm cable protected by 10amp breaker. - C2
  • No RCD protection on any circuits - C1
  • Sub Board for cooker dangerously wired incorrectly and in 6mm single insulated
cable - C1

Thanks for your help.
 
None of those C1 codes are worthy of such a code in my opinion. C1 dangers should be rectified immediately and the inspection halted until they are or a danger notice issued.
I'd doubt the professionalism and or ability of the inspector.
 
None of those C1 codes are worthy of such a code in my opinion. C1 dangers should be rectified immediately and the inspection halted until they are or a danger notice issued.
I'd doubt the professionalism and or ability of the inspector.
Thanks Andy. I thought they might have been a bit over zealous with the C1’s (slightly suspicious about their impartiality as they were affiliated with a building contractor who also came at the same time to quote for other work the buyers want done, so may have a bit of a vested interest in saying a load of work needs doing). Also thought it was odd they didn’t say anything to me about anything dangerous at the time they did the inspection as I was there (with kids) and I’ve only been given a copy of the report now because I asked for it after the buyer raised concerns.
 
I have the impression whoever wrote the report is either (a) angling for lots of remedial work, or (b) being unduly harsh perhaps because they were asked to be, or (c) has absolutely no idea what they are doing.

What people writing these reports perhaps don't realise, if they code something that shouldn't be coded, and cause someone to pay for unnecessary work, they might leave themselves open to legal action and perhaps be liable for those costs.
 

Reply to Advice on EICR fail in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hello I live in a rental in scotland and have recently had an EICR carried out. I have an old fuse wire fuse board on a wooden plate with no rcd...
Replies
4
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Evening all, I found my first ever split concentric cable today. Running from an isolator up and into a flat. I was doing an EICR. I could not...
Replies
7
Views
1K
My parents had an EICR completed after a change of tenant in the shop and flat property, this took place March 2021. The summary of the report...
Replies
35
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock