Yeah I said it’s Debatable, and yes I should have said “Inspection and Testing” . At the end of the day they’ve obviously not did the tug test when 2nd fixing and the result is the line cable came out when the socket was disturbed.You got a disagree because testing would have not likely shown this up, proper inspection might have.
I’ve tested numerous ring circuits and most are usually ok, but there have been a few with “open” continuity on either line, neutral or earth or even all! Some with significant difference between line and neutral or earth eg N = 0.65ohms but live would be say 200ohms! Obviously not open, but a slight touching contact at some point in the circuit.