Absence of RCD (411.5.2; 531.2 C3
Absence of RCD 421.4.9; 543.2 C3
Accessory damaged 421.1.3 c2
Inconsistent resistance values for ring circuits F1
Characteristic of supply do not conform to industry standards 612.3.2 F1
Insulated cable not taken inside the enclosure of an assessor 412 C2

This what he has said in the report for a safety certificate

C3 is improvement recommended only, so technically you are not required to have anything done for these items to achieve a satisfactory report. What I find interesting is the regulations stated there... 411.5.2 relates to TT earthing systems (what does the report claim your earthing system is?), 531.2 relates to selection of equipment and outlines some key characteristics of the RCDs we are supposed to use, 421.4.9 does not exist in the regs (this may be a typo) and 543.2 details the different types of protective conductor and what is allowable in terms of their implementation and is nothing to do with RCDs.

Accessory damaged C2, this is a legitimate item that requires work providing the item is actually damaged.

Inconsistent resistance values for ring final circuits, Further Investigation. Whether this requires further attention depends largely on what this statement means. If the values are varying by say 0.01 ohms between tests, this could simply be due to the tolerances of the test equipment in use, certainly I wouldn't be worried about it. But if say, r1 is radically different from rn or r2 is way off roughly 1.667 x r1 (or rn), then there could be a bad connection which needs to be investigated to ensure the ring is safe for continued operation. Has he supplied the values of r1, rn and r2 for the RFCs in question?

Characteristic of supply do not conform to industry standard 612.3.2... interesting... 612.3.2 in the regs relates to what constitutes acceptable values for insulation resistance test results and has nothing to do with the characteristics of the supply (which include things like 230v nominal voltage, 50Hz nominal frequency and other important values). So I have absolutely zero clue what he's getting at with this other than possibly just BS to justify charging you an indeterminate fee for investigating a problem which may not actually exist.

The insulation not taken inside an enclosure, yes, that can be a problem but it depends on where it is and what it is as to whether you can legitimately do anything about it. If it's in the meter cupboard for example, you're not responsible for much of what's in there and fixing some of it may require the presence of the seal fairy to cut the seals off the meter/service head (we're not supposed to do that).

You want it to be safe, but with the limited information available, I'd say this guy is a chancer trying to take you for a ride.

Definitely, find a spark from the forums who is local to you and take the advice the guys have given you... get a second opinion from someone else. This could be either a brand new EICR (don't got for a cheap one, on your average house, I look to be there all day and would charge around £240) or engage someone to work through the report and double check what the original guy has put down (as I said, I've done that for someone for a house sale and it cost them around £120 plus materials - in that case, the guy made some very dodgy claims about work that supposedly needed doing and the suggested remedy included a new consumer unit which would have resulted in a bill significantly higher). And of course, please come back and let us know how it turns out.
 
411.5.2 indicates a TT system and if this is the case I would think a C3 inappropriate.
421.4.9 is not a Regulation at all unless my eyes deceive me.
543.2 has nothing to do with rcds.
421.1.3 has little do do with damaged accessories.
612.3.2 makes no reference to characteristics of the supply.

Beaten to it by @westward10 :D
 
It is all very well composing "technical" Reports, maybe not in this case, if the client is technical in such matters and not a layperson but if you are going to quote Regulations make sure they are correct.
 
C3 is improvement recommended only, so technically you are not required to have anything done for these items to achieve a satisfactory report. What I find interesting is the regulations stated there... 411.5.2 relates to TT earthing systems (what does the report claim your earthing system is?), 531.2 relates to selection of equipment and outlines some key characteristics of the RCDs we are supposed to use, 421.4.9 does not exist in the regs (this may be a typo) and 543.2 details the different types of protective conductor and what is allowable in terms of their implementation and is nothing to do with RCDs.

Accessory damaged C2, this is a legitimate item that requires work providing the item is actually damaged.

Inconsistent resistance values for ring final circuits, Further Investigation. Whether this requires further attention depends largely on what this statement means. If the values are varying by say 0.01 ohms between tests, this could simply be due to the tolerances of the test equipment in use, certainly I wouldn't be worried about it. But if say, r1 is radically different from rn or r2 is way off roughly 1.667 x r1 (or rn), then there could be a bad connection which needs to be investigated to ensure the ring is safe for continued operation. Has he supplied the values of r1, rn and r2 for the RFCs in question?

Characteristic of supply do not conform to industry standard 612.3.2... interesting... 612.3.2 in the regs relates to what constitutes acceptable values for insulation resistance test results and has nothing to do with the characteristics of the supply (which include things like 230v nominal voltage, 50Hz nominal frequency and other important values). So I have absolutely zero clue what he's getting at with this other than possibly just BS to justify charging you an indeterminate fee for investigating a problem which may not actually exist.

The insulation not taken inside an enclosure, yes, that can be a problem but it depends on where it is and what it is as to whether you can legitimately do anything about it. If it's in the meter cupboard for example, you're not responsible for much of what's in there and fixing some of it may require the presence of the seal fairy to cut the seals off the meter/service head (we're not supposed to do that).

You want it to be safe, but with the limited information available, I'd say this guy is a chancer trying to take you for a ride.

Definitely, find a spark from the forums who is local to you and take the advice the guys have given you... get a second opinion from someone else. This could be either a brand new EICR (don't got for a cheap one, on your average house, I look to be there all day and would charge around £240) or engage someone to work through the report and double check what the original guy has put down (as I said, I've done that for someone for a house sale and it cost them around £120 plus materials - in that case, the guy made some very dodgy claims about work that supposedly needed doing and the suggested remedy included a new consumer unit which would have resulted in a bill significantly higher). And of course, please come back and let us know how it turns out.

Thank you for all that. How do I find a sparky near me!! I am in Kingston upon Thames!

Thank you for all that and taking the time and trouble to work through it!

I will get another quote or at least get a sparky to go over his report.
 
411.5.2 indicates a TT system and if this is the case I would think a C3 inappropriate.
421.4.9 is not a Regulation at all unless my eyes deceive me.
543.2 has nothing to do with rcds.
421.1.3 has little do do with damaged accessories.
612.3.2 makes no reference to characteristics of the supply.

Good job mate :)
Let those who wish to quote regs read the good book first !
 
To find one of us who may be near you, take a look here:-

Find an Electrician, Plumber or Tiler | Electricians Forum - Talk electrics and electricals with fellow professional electricians - http://www.electriciansforums.co.uk/categories/find-an-electrician-plumber-or-tiler.84/

You then have two options... you can go to the directory section and search I believe or you could post in the Looking for a domestic electrician section with a rough idea of the job.

You might be advised if you use the directory, to check they have recently been active... then at least if they make a hash of it you can come back tell us all about it and we can proceed to ridicule them into doing the job properly :)

Good luck.
 
problem with the electricians directory is that a lot of them aren't even forum members.
 
Don't get electricians through estate agents either. They probably get a kick back.....

Partly disagree there Murdoch. I know several estate agents whom I get work from, no kickbacks whatsoever. I also know other trades that also do work through estate agents with the same outcome. I know this because one is a gas lad and the other a painter and I am pretty pally with them.

Obviously it does go on though.
 
Absence of RCD (411.5.2; 531.2 C3
Absence of RCD 421.4.9; 543.2 C3
Accessory damaged 421.1.3 c2
Inconsistent resistance values for ring circuits F1
Characteristic of supply do not conform to industry standards 612.3.2 F1
Insulated cable not taken inside the enclosure of an assessor 412 C2

This what he has said in the report for a safety certificate
Whereabouts in Surrey are you?

Hampton Wick near Kingston upon Thames
 
Some agents don't add a markup for themselves, some do. I used to work for one that took 15% for themsevles, plus added VAT to the bill even though I don't charge VAT. In this case I had one or two of the landlords wanting me to work directly for them, to save them around 35%.
 

Reply to Am I being taken for a ride? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
173
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K
Hi all, am new here. My wife and I let a small house which requires an EICR due to the new regs. The management agent organised for an...
Replies
34
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock