Absence of RCD (411.5.2; 531.2 C3
Absence of RCD 421.4.9; 543.2 C3
Accessory damaged 421.1.3 c2
Inconsistent resistance values for ring circuits F1
Characteristic of supply do not conform to industry standards 612.3.2 F1
Insulated cable not taken inside the enclosure of an assessor 412 C2
This what he has said in the report for a safety certificate
C3 is improvement recommended only, so technically you are not required to have anything done for these items to achieve a satisfactory report. What I find interesting is the regulations stated there... 411.5.2 relates to TT earthing systems (what does the report claim your earthing system is?), 531.2 relates to selection of equipment and outlines some key characteristics of the RCDs we are supposed to use, 421.4.9 does not exist in the regs (this may be a typo) and 543.2 details the different types of protective conductor and what is allowable in terms of their implementation and is nothing to do with RCDs.
Accessory damaged C2, this is a legitimate item that requires work providing the item is actually damaged.
Inconsistent resistance values for ring final circuits, Further Investigation. Whether this requires further attention depends largely on what this statement means. If the values are varying by say 0.01 ohms between tests, this could simply be due to the tolerances of the test equipment in use, certainly I wouldn't be worried about it. But if say, r1 is radically different from rn or r2 is way off roughly 1.667 x r1 (or rn), then there could be a bad connection which needs to be investigated to ensure the ring is safe for continued operation. Has he supplied the values of r1, rn and r2 for the RFCs in question?
Characteristic of supply do not conform to industry standard 612.3.2... interesting... 612.3.2 in the regs relates to what constitutes acceptable values for insulation resistance test results and has nothing to do with the characteristics of the supply (which include things like 230v nominal voltage, 50Hz nominal frequency and other important values). So I have absolutely zero clue what he's getting at with this other than possibly just BS to justify charging you an indeterminate fee for investigating a problem which may not actually exist.
The insulation not taken inside an enclosure, yes, that can be a problem but it depends on where it is and what it is as to whether you can legitimately do anything about it. If it's in the meter cupboard for example, you're not responsible for much of what's in there and fixing some of it may require the presence of the seal fairy to cut the seals off the meter/service head (we're not supposed to do that).
You want it to be safe, but with the limited information available, I'd say this guy is a chancer trying to take you for a ride.
Definitely, find a spark from the forums who is local to you and take the advice the guys have given you... get a second opinion from someone else. This could be either a brand new EICR (don't got for a cheap one, on your average house, I look to be there all day and would charge around £240) or engage someone to work through the report and double check what the original guy has put down (as I said, I've done that for someone for a house sale and it cost them around £120 plus materials - in that case, the guy made some very dodgy claims about work that supposedly needed doing and the suggested remedy included a new consumer unit which would have resulted in a bill significantly higher). And of course, please come back and let us know how it turns out.