maddad2001

Hi

has anyone recently done the am2? I just wanted a basic calculation for setting the overload (they give you motor rating in Kw) for the 3 phase dol motor. I have tried looking this up for last few nights, but keep getting inconsistent or over complicated findings.

and people at work say 'sorry mate it's been along-time since I worked that out, it should say on the motor plate'. But the assessor doesn't provide you a motor plate, just tells you the kw of starter/motor. I tried to find the answer myself, but I'm unsure and bit worried about this, mainly due to different interpretations. If anyone can help it would be hugely appreciated.

thanks for reading this.
 
work out the phase current, taking p.f. into account, then set overload 10% over.
 
For a start you DO NOT set at +10%. You set at 100%. The O/L unit is designed to take start up in to account.

KW/3/(U/√3)/PF=A

So for 5KW
5000/3/230/.9=7.2A

If the PF isn’t given assume .9 (ask first if you need to take this in to account)

The +10% or even +25% settings went out with the ark.
 
Last edited by a moderator:
The Kw rating rating of a motor is the actual available turning power given in mechanical terms at the shaft .. note its not an electrical quantity, its a modern version of horsepower hence you problem finding a relative link ... the FLC (full load current) of a motor is what it will use to generate this mechanical power.

Any motor you connect direct on line will have a plate stating its FLC at a supplied voltage you are using and this is the setting of your O/L that Tony has quite rightly expressed, this is for direct on line starting only when other starting methods are used then the rules can change.... Im a little disturbed if the college is giving you only a KW rating and expecting you to know how to set the O/L .... I suspect you will find 2 values on the motor plate for each winding config' and you choose the one your using ...probably 400v in your case but ask someone who has done the exam in the training area.to confirm this as our many yrs of experience can give an over complicated answer to your query.

In tels defense the old ancient O/L pot were not as accurate as modern ones and the likes of the oil filled ones etc had to have a rule of thumb allowance applied hence his suggestion.. but he did see the birth of electricity :smilewinkgrin:

Just to add to the above the efficiency of the motor needs to be added to the calculations for accuracy too although its often skipped.
 
Last edited:
OK I should have included efficiency in the calculation which is the relationship of shaft KW to power input. That unfortunately isn’t a linear graph.
That information can only be obtained from the manufacturer or by calculation from the figures on the makers plate, which our OP won’t have access to.

Not knowing the precise requirements of the examination it’s hard to know where to stop.


DW
Dashpot O/L’s are old technology, but they’re still out there.

For motors you only set above 100% if the manufacturer recommends it. I’ve worked on dash pot O/L’s that have dated from the 1930’s to the 1970’s. They were all different.

It’s when they are linked to CT’s the fun and games really start because they are just marked in %, typically 70% to 130%. When the CT ratio is 2500/5 the sphincter starts twitching a bit.
Then there’s the minor problem of time delay, adjustable by the bleed through rate or oil viscosity. Silicon oil was available in 100, 200, 500 and 1000cS (Stokes are a measure of viscosity), blending it is an art in itself.

It’s one of the classic cases of RTFM. If you can find one.
 
Last edited by a moderator:
Becoming far too complicated, "Linear graphs" / "Motor efficiency" / "Bleed through rates" / "CT ratios" / etc,etc. With DOL motors(the vast majority are) set the overload at the stated nameplate FLC as long as supply voltage and motor voltage are the same. Thermal overloads are how accurate anyway ? You could argue all day about the precise setting of individual motors, can,t help thinking people are just showcasing their knowledge here, sorry.
 
Becoming far too complicated, "Linear graphs" / "Motor efficiency" / "Bleed through rates" / "CT ratios" / etc,etc. With DOL motors(the vast majority are) set the overload at the stated nameplate FLC as long as supply voltage and motor voltage are the same. Thermal overloads are how accurate anyway ? You could argue all day about the precise setting of individual motors, can,t help thinking people are just showcasing their knowledge here, sorry.

Have to say I think all the contributions, including yours, are valid. It's good to see the rationale/detailed explanation as well as the quick "do it this way & it'll be ok". And so a bit of "here's what I know" does no real harm:smilewinkgrin:
 
right or wrong, i was taught the 10% over to allow for uncalculated losses, like not knowing the exact pf and efficiency figures. i defer to tony's greater knowledge esp. with bigger motors.
 
Becoming far too complicated, "Linear graphs" / "Motor efficiency" / "Bleed through rates" / "CT ratios" / etc,etc. With DOL motors(the vast majority are) set the overload at the stated nameplate FLC as long as supply voltage and motor voltage are the same. Thermal overloads are how accurate anyway ? You could argue all day about the precise setting of individual motors, can,t help thinking people are just showcasing their knowledge here, sorry.

I gave the simplest calculation in my first post, it should do for any examination. The examiners can’t ask for more without giving the full details of the motor. That would defeat the object of the examination.
Read the makers plate, set the O/L. It would be that easy.

Motors, O/L’s and control have been my bread and butter for 40 years. If anyone wants to learn then I’m more than willing to go in to detail on a one to one basis.
 
I gave the simplest calculation in my first post, it should do for any examination. The examiners can’t ask for more without giving the full details of the motor. That would defeat the object of the examination.
Read the makers plate, set the O/L. It would be that easy.

Motors, O/L’s and control have been my bread and butter for 40 years. If anyone wants to learn then I’m more than willing to go in to detail on a one to one basis.

Read the maker,s plate set the o/l to FLC it IS that easy, in the vast majority of cases. I just feel this subject can be made too complex when really there is no need. I don,t disagree with the post either referring to a 110% setting, as the argument between nuisance trips and motor safety is another one where there is no definitive. Motors and control gear have also been my bread and butter for around 40yrs though I do not claim to have anything like the detailed knowledge you have and I mean that with the greatest of respect.
 
Read the maker,s plate set the o/l to FLC it IS that easy, in the vast majority of cases. I just feel this subject can be made too complex when really there is no need. I don,t disagree with the post either referring to a 110% setting, as the argument between nuisance trips and motor safety is another one where there is no definitive. Motors and control gear have also been my bread and butter for around 40yrs though I do not claim to have anything like the detailed knowledge you have and I mean that with the greatest of respect.

The OP has stated that the data plate is not available, only the KW rating
 
Ask for the power factor of the motor. Then calculate as follows -

EXAMPLE!!!

1.5Kw Power of the motor (will be written on it)

over

1.732 (square root of 3, 3 phase) x 415 (voltage) x 0.8 (example of the power factor he might give you).

1500 / 1.732 X 415 X 0.8 (575.024) = 2.60
 
I read up on the newer AM2 test the plate doesn't exist to take a value off because they don't have a motor it a box with terminals pretending to be a motor, also to note the harder sections of the AM2 have been dropped... no more steel conduit to a light fitting to bend which was the key area of failure in my day...I mean really dont understand why they bother doing it anymore its been simplified that much might as well give them a pass because they found the exam center!
 
I read up on the newer AM2 test the plate doesn't exist to take a value off because they don't have a motor it a box with terminals pretending to be a motor, also to note the harder sections of the AM2 have been dropped... no more steel conduit to a light fitting to bend which was the key area of failure in my day...I mean really dont understand why they bother doing it anymore its been simplified that much might as well give them a pass because they found the exam center!

I visited a test centre last year for a look, the new AM2 is nowhere near at the standard it once was. In fact I thought it was a bit of a joke.

As for the motor, in the exam. It is now wired to terminals on a box. Efficiency doesn't come into play.
 
In a nutshell the practical has become a joke.

3way lighting.
ring final.
smoke alarm in fp200.
s-plan heating circuit.
a run of cat 5
SWA to a 3ph socket
A motor circuit, all DOL control pre wired.



All the containment is pre installed. Wiring diagrams are provided. All MCB sizes and positions in the board are pre defined.

So long as you follow written instruction, it's an easy pass. There are even pre built rigs candidates can look at.
 
I did the previous version of the AM2 and I found it to be an easy and enjoyable few days! Working in perfect working conditions with decent materials and a plan that actually made sense!
And we had a real motor which went round and round when we turned it on!
 
The power lab at the engineering collage I went to was shut down by the HSE.
60HP DOL? No problem. But far too dangerous for today’s little darlings.

My son went to the same collage and was quite looking forward to getting to play in the lab. He was to be disappointed.

FFS you went to work the next day, all of a sudden you have to deal with it.
 
It's interesting how a lot of people on here 'play down' the new AM2. I've recently passed it and feel quite proud of my achievement. Remember this test is aimed at those who are nearing the end of their 4th year as an apprentice, not fully fledged sparks who have been in the game for years.

Would be interesting to see how many of the old timers would get through it first time, bad habits and all that :smilewinkgrin:
 
You should be damn well near fully fledged at 4 years in, and certainly able to do your own jobs with minimal supervision.

And there's no room left for bad habits on the new AM2, it's all wire by numbers isn't it? There was precious little you could do wrong on the old one really if you knew what you were doing and could read!
 
It's interesting how a lot of people on here 'play down' the new AM2. I've recently passed it and feel quite proud of my achievement. Remember this test is aimed at those who are nearing the end of their 4th year as an apprentice, not fully fledged sparks who have been in the game for years.

Would be interesting to see how many of the old timers would get through it first time, bad habits and all that :smilewinkgrin:


I played it down because I read the requirements and TBH its been made a lot easier ... as I said the key points that most failed in my day have been dropped, you had to make a steel dogs leg bend and the conduit you were given was probably 10mm longer than required so very little room for error ... it really does explain why half my apprentices over the yrs passed the AM2 but couldn't bend conduit... its a skill required to be a competent Electrician unless you want to basically hold the title of domestic installer who would not really ever need it.

When you simplify things the level of skill entering the Electrical world also drops in line too this is not a dig at those taking the exams your a victim of a dumbed down education system which started collapsing when physical punishments were banned in state schools in 86 if I recall, we now have an unhealthy schooling environment where disruption is destroying education and leaving the UK at the bottom of the education standards in the world with regards to sciences and maths... Noted 2 key areas to becoming an Electrician.

Yes be proud of your pass Im not trying to take that away but you were educated in a very disruptive environment and sometimes had to revise harder to achieve less so the knock on effect was all further educations systems had to be dumbed down too or no-one could pass them, this isn't my opinion this has been shown to be the case and education levels have dropped year in year out but pass rates increased which sound counter-intuitive but government after government had to hide the reality to avoid the blame its only recently that changes are now been made in schools and in some ares reverting back to the old ways. Ill stand by what I posted then but understand its not an attack on anyone taking these exams and after teaching apprentices for 20yrs and helping and guiding them do you really think I'd struggle with the AM2 as it is now, Im not one to get bad habits as it puts either your or the public at risk.
 
Our apprentices came to us after a year of full time collage.

If after 6 months on the works they couldn’t rattle that lot off I’d want to what they were doing.

I’m sorry but as a test of any form of competence it is a total farce.
 
It's interesting how a lot of people on here 'play down' the new AM2. I've recently passed it and feel quite proud of my achievement. Remember this test is aimed at those who are nearing the end of their 4th year as an apprentice, not fully fledged sparks who have been in the game for years.

Would be interesting to see how many of the old timers would get through it first time, bad habits and all that :smilewinkgrin:

BTW they’re not bad habits.

Because we don’t need a crib sheet to work to they equate to “knowing your job” or “how to get results with the minimum of downtime”.

Believe it or not ultimately your wages depends on what goes out the door.
 
why no actual motor to connect to in the am2?
would it not give the guys taking it a better idea of what they are trying to achieve?
off the top of my head my am2 consisted of
steel trunking to the top of already fitted db first.
20mm be conduit with a double 90 bend and a set into trunking.
25mm be conduit with a bubble ( could have fitted your head through mine but it fitted somehow!)
4l1.5 micc
2h6.00 micc
wiring the lighting circuit and a fwd rev starter
a bit of cable tray also.
very few passed it first time.
the lads with the big teams flew through the conduit , trunking and tray but came unstuck on the wiring and testing.
the lads with the smaller contractors were the opposite from the above.
my lasting memory was a lad from bk drilling his thumb and having to go to hospital!
and we are being told its not dumbed down.....
 
maddad2001

Please let us know how you go on.


Well I passed the exam, seeing as most of you think the exam is a doddle. Guess I shouldn't be too proud of myself.

Just remember most of my apprenticeship has been in the recession. Finding jobs is hard to come by for new starters in some regions. I havent had exposure to much proper testing and the exam is quite thorough testing wise. Also I dont recieve any where near the amount of installation practise and variety I would like. Im am older apprentice in my 20s and unfortunately jumping from firm to firm is not a safe solution for me. Because I wouldn't gamble on my kids livelihoods. But lots of companies are employing young guys with no intention of correctly training them mainly using them as cheap labourers.
 
Its a generation thing don't be offended, its also harder to learn in the disruptive environment in schools nowadays hence half the reason they had to simplify it... it doesn't mean it was easier for you to sit the exam so congratulations on your Pass ... a proud moment for any student/Electrician
 
Wattage/693=amps

Old thread but still relevant even today, could you please expand on your equation, where do you get the value 693 from and what exactly is this formula relating to, as we are discussing standard 3ph induction motors can I assume you are referring to these to apply the calculation?
 
400*sqrt(3) = 693. Or, if you prefer, 3*230 with a rounding error! Watts per amp of line current into a 3-phase resistive load.
 
400*sqrt(3) = 693. Or, if you prefer, 3*230 with a rounding error! Watts per amp of line current into a 3-phase resistive load.

I was holding a carrot out for feedback, wondered why he had posted it in a thread about motors so I took a position of confusion, idea was for him to look it up and realise he had posted the wrong formula (best way to learn imho), my response back to his reply would have corrected him regarding resistive load calcs against that of an inductive motor calc' but he never posted a reply and I forgot about it...:confused:
 

Reply to am2 motor overload in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
701
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
Replies
19
Views
5K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi everyone, I’m doing my am2 and can’t seem to find a definite calculation to working out the overload this equation I = P/V/1.73/0.8 has popped...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock