Discuss Amendment 3 DPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

1st of Jan 2015, in full effect by 1st of July 2015

Just another bloody regs book really innit, all because a few plebs up at the IET want to correct their spelling mistakes! lol
 
What's this all about?
(See 411.4 etc.)

Cmin is the minimum voltage factor to take account of voltage variations depending on time and place, changing
of transformer taps and other considerations.
NOTE 1: For a low voltage supply given in accordance with the Electricity Safety, Quality and Continuity Regulations
2002 as amended, Cmin is given the value 0.95.
 
Also, have a look at the altered tabulated max Zs values for B, C and D curve 60898s!

What a ball ache, that means the big green book is gonna have to come out every time I fill in a cert now!
 
This is to take account of the lower end of the range of the tolerances and VD of a nominal 230V/400 supply, if you notice they have also re-calculated the max Zs values (OCPD tables etc.) to take this into account too.

What gets me with this is that they already lowered these once to "harmonise" the 230/400 calcs (from 240/415), this new lowering probably makes some sense if you have a "real" 230/400 supply which we don't (we only changed the tolerance band) unless we are really lowering our supply voltage this time ?

More significantly, the commercial/industrial supervised person "get out clause" for RCDs has all but been removed, unless you are prepared to sign a RA to say otherwise, I cannot see many people wanting to sign that.
This will cause some problems with offices and the like.

Where does all this Bull Shine end ?, yet they do nothing to correct all the other anomalies and poor wording of existing regs, just add more Sh*t on top, was the 17th that bad ?

More money for "the boys", I wish we would tell Europe to P*ss off and fit in with us for a change.
 
Last edited:
This is to take account of the lower end of the range of the tolerances and VD of a nominal 230V/400 supply, if you notice they have also re-calculated the max Zs values (OCPD tables etc.) to take this into account too.

What gets me with this is that they already lowered these once to "harmonise" the 230/400 calcs (from 240/415), this new lowering probably makes some sense if you have a "real" 230/400 supply which we don't (we only changed the tolerance band) unless we are really lowering our supply voltage this time ?

More significantly, the commercial/industrial supervised person "get out clause" for RCDs has all but been removed, unless you are prepared to sign a RA to say otherwise, I cannot see many people wanting to sign that.
This will cause some problems with offices and the like.

I bet DI EICs with RAs attached will be flying out of the printer! they do love a get out clause don't they!
 
To be honest D I am p*sed off with the whole lot, More books to be replaced, GNs etc. then we will sure to be having the 18th ed next, more costs for exams etc. IET and C&G on a good old money spinner, I know we have always had updates, mostly for the better, I agree with the 17th for RCDs in domestic for example, but this just takes the p*ss.

This is more to fit in with the poxy EU, it is more of a political change IMO, rather than for good Electrical reasons.
 
Last edited:

Reply to Amendment 3 DPC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Eh up :) I've done some new PDF forms for BS7671 18th Edition Amendment 2 2022 (the Big Brown Book), based on the IET model forms. You can fill...
Replies
27
Views
12K
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
Just been reading an article regards Amendment 2 coming out next year. The requirements for AFDD is going to create some interesting conversations...
Replies
35
Views
4K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
461

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock