I use an old Kyoritsu analogue multimeter. It's always been reliable and accurate and I picked it up for next to nothing at a stall on a market. Maybe keep an eye on Gumtree or similar classified advertisements sites, analogue testers aren't fashionable because they don't sync with facebook and instagram so youngsters nowadays won't touch them with a bargepole. If you bide your time and keep your eyes peeled you'll get one for a song.
Here in UK, car boot sales are sometimes a good source for all sorts of bargains including electrical gear.

Somewhat off topic but we picked up a new DVD player, still in the original box and complete with manual for just a fiver. A whole box of cable ties for 50p. A digital multimeter for a quid.
 
Beware that many cheap multimeters, analogue and digital, won't comply with GS38 and will be unsafe for testing electrical installations due to the level of potential fault currents and voltage spikes. If all you want to do is prove whether a 230V supply is real or phantom, a test lamp will do just fine:

Drummond Test Lamp Mtl7 150-500 Ac/dc New Without Packaging | eBay

MTL7 DRUMMOND Test Lamp New and sealed. | eBay

With fused test leads they will comply.
 
Would any analog voltage tester be suitable for testing to see if real or phantom voltage? Everyone seems to be mentioning the older types (i.e Avo8 etc), would a new analog multimeter still do the job?

For example:

GENERAL PURPOSE ANALOGUE AC DC MULTIMETER VOLTMETER NEW | eBay
It really depends on how they have managed the electronics inside the meter.
The old style analog meters had a high resistance in series and this gives a voltage reading across the resistance but there is some flow of current acros this resistance that will (very slightly) drop the votlage and give a lower reading.
However modern meters use electronics to create a practically infinite resistance against which to measure the voltage, this gives accurate values of voltage without any loss through the resistance, however this is very definitely the unloaded voltage and this means the presence of a large potential difference with no capability of supplying current will register as a voltage even though for all practical purposes there is no voltage present.

If the meter manufacturer uses a modern infinite resistance system and uses electronics to transfer this to a needle on a meter dial then it would be the same as any modern unit.
I do not know the availability of standard chips that would make this construction straightforward but I would expect the cost would be greater than a standard analogue arrangement so the ease of making a basic deflection meter means that they probably would not bother and that a modern analogue meter would be fine.
However others may know different.
 
The point is this. What you need to confirm that a voltage is 'real', not phantom, is a meter or indicator that loads the supply sufficiently. The figure that matters is its input impedance; a low input impedance will load the circuit under test and pull down a phantom voltage to a level close to zero. A 'real' fault will be unaffected and the full supply voltage will be indicated.

Clearly, a test lamp will load the supply as it has (relatively) a much lower resistance than the inductive or capacitive 'fault' and will try to draw much more current than a phantom voltage will supply. 'Simple' analogue meters will also load the supply to a greater or lesser extent.

Digital meters and the 'better' analogue ones will have a high impedance, which is exactly what you need for most electronics work, so that the meter doesn't significantly affect the voltage you're trying to measure.

The Fluke TL225 / SV225 mentioned by Marvo puts a 3kohm resistor across the circuit being measured so that a high impedance meter behaves like a low impedance one.



(I've covered some of the same ground as Richard Burns but I thought it worth saying anyway.)
 
Last edited:
It really depends on how they have managed the electronics inside the meter.
The old style analog meters had a high resistance in series and this gives a voltage reading across the resistance but there is some flow of current acros this resistance that will (very slightly) drop the votlage and give a lower reading.
However modern meters use electronics to create a practically infinite resistance against which to measure the voltage, this gives accurate values of voltage without any loss through the resistance, however this is very definitely the unloaded voltage and this means the presence of a large potential difference with no capability of supplying current will register as a voltage even though for all practical purposes there is no voltage present.

If the meter manufacturer uses a modern infinite resistance system and uses electronics to transfer this to a needle on a meter dial then it would be the same as any modern unit.
I do not know the availability of standard chips that would make this construction straightforward but I would expect the cost would be greater than a standard analogue arrangement so the ease of making a basic deflection meter means that they probably would not bother and that a modern analogue meter would be fine.
However others may know different.
thanks rich for the very informative post
 
you'd put the resistor in parallel with the leads. that would then drain phantom voltage that the dmm won't.
 
Thanks all for the advice.

I have decided to go for the Drummond mtl20! Thanks Handy Sparks :smile5:
 
you'd put the resistor in parallel with the leads. that would then drain phantom voltage that the dmm won't.
Spot on :)

You'll have a job doing this and still having a "safe" instrument/set of leads. Could probably do it with a plug-in box - but it's a lot of work when you could buy a Drummond :)
 
Any approved voltage indicator (AVI) should differentiate between a ghost and a real voltage.
I'd love to believe this. The input impedance of my Martindale isn't quoted, but the manual says, "Test current: <3.5mA at 600V" which implies an input impedance of at least 170k. Not the 1M (or even 10M) of a DMM, but pretty close. The Drummond also pulls "<3.5mA" unless you press the button, in which case it will draw "28mA @ 240V AC, 60mA @ 500V AC."... Zin ~ 8k. Fluke's Lo-Z function is "about 3k" (according to Fluke literature).

Also, I have a Dilog voltage indicator, it bleeps and warbles and lights up like a Christmas tree when touching anything conductive vaguely close to something that might be energised. (Which is why I bought the Martindale).

So, although not doubting what you say, I am left a little confused! :)
 
Last edited:
I'd love to believe this. The input impedance of my Martindale isn't quoted, but the manual says, "Test current: <3.5mA at 600V" which implies an input impedance of at least 170k. Not the 1M (or even 10M) of a DMM, but pretty close. The Drummond also pulls "<3.5mA" unless you press the button, in which case it will draw "28mA @ 240V AC, 60mA @ 500V AC."... Zin ~ 8k. Fluke's Lo-Z function is "about 3k" (according to Fluke literature).

Also, I have a Dilog voltage indicator, it bleeps and warbles and lights up like a Christmas tree when touching anything conductive vaguely close to something that might be energised. (Which is why I bought the Martindale).

So, although not doubting what you say, I am left a little confused! :)

Which dilog AVI are you using? I have always used the combivolt ones and they show a clear different result when detecting real and ghost voltages.

I agree the noises can be the same but if it is real then the red LEDs illuminate up to the nominal voltage present, wheras ghosts only light the single red LED.

As with any test equipment you have to learn to use it correctly and how to interpret the readings.
 
Which dilog AVI are you using? I have always used the combivolt ones
Yep, that's the chicken. (Well, combivolt twos...)

As with any test equipment you have to learn to use it correctly and how to interpret the readings.
Well that's me told. Guess I've got some more learning to do. :)

Cheers. :)
 

Reply to Analog voltage tester? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hi all, Firstly I am new to the forum, so will start by saying hi. I work as an electricians mate, and am joining the forum to gain experience...
Replies
3
Views
658
Hello, I just started in the trade 3 months ago and have been told I need tools such as testers, could someone let me know whether it would be...
Replies
4
Views
623
Hi there, wondering if anyone can give me some advice please. In my kitchen I have a cooker switch with a plug socket which I believe is on a...
Replies
4
Views
2K
Hi I’m just starting to do ev chargers so it’s looks like I need new tester. I currently have Megger 1711. So I can’t do a 6ma rcddc test. I...
Replies
3
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock