K
Knobhead
well we still need entries in the trainee area lol
Marvo won't let me in.
Discuss Analog voltage tester? in the UK Electrical Forum area at ElectriciansForums.net
well we still need entries in the trainee area lol
Here in UK, car boot sales are sometimes a good source for all sorts of bargains including electrical gear.I use an old Kyoritsu analogue multimeter. It's always been reliable and accurate and I picked it up for next to nothing at a stall on a market. Maybe keep an eye on Gumtree or similar classified advertisements sites, analogue testers aren't fashionable because they don't sync with facebook and instagram so youngsters nowadays won't touch them with a bargepole. If you bide your time and keep your eyes peeled you'll get one for a song.
Beware that many cheap multimeters, analogue and digital, won't comply with GS38 and will be unsafe for testing electrical installations due to the level of potential fault currents and voltage spikes. If all you want to do is prove whether a 230V supply is real or phantom, a test lamp will do just fine:
Drummond Test Lamp Mtl7 150-500 Ac/dc New Without Packaging | eBay
MTL7 DRUMMOND Test Lamp New and sealed. | eBay
It really depends on how they have managed the electronics inside the meter.Would any analog voltage tester be suitable for testing to see if real or phantom voltage? Everyone seems to be mentioning the older types (i.e Avo8 etc), would a new analog multimeter still do the job?
For example:
GENERAL PURPOSE ANALOGUE AC DC MULTIMETER VOLTMETER NEW | eBay
thanks rich for the very informative postIt really depends on how they have managed the electronics inside the meter.
The old style analog meters had a high resistance in series and this gives a voltage reading across the resistance but there is some flow of current acros this resistance that will (very slightly) drop the votlage and give a lower reading.
However modern meters use electronics to create a practically infinite resistance against which to measure the voltage, this gives accurate values of voltage without any loss through the resistance, however this is very definitely the unloaded voltage and this means the presence of a large potential difference with no capability of supplying current will register as a voltage even though for all practical purposes there is no voltage present.
If the meter manufacturer uses a modern infinite resistance system and uses electronics to transfer this to a needle on a meter dial then it would be the same as any modern unit.
I do not know the availability of standard chips that would make this construction straightforward but I would expect the cost would be greater than a standard analogue arrangement so the ease of making a basic deflection meter means that they probably would not bother and that a modern analogue meter would be fine.
However others may know different.
could always put a resistor across the leadsThis is one reason I recommend the Fluke 117 as an electricians meter (although not analogue) as it has a lowZ setting of which eliminates ghost voltages.
Reply to Analog voltage tester? in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.